Morning all,
Possibly a simple question But a mix of doctor prescribed medication and post Wembley joy have left my brain elsewhere.
I have a sub DB that needs the supply isolating if a fire is detected (commercial Kitchen) So The 3 phase supply for this DB needs a 4P contactor. Do I size the contactor to the current load of the sub board(10A) so Say a 20A contactor.
Or do I need to size the contactor to 63A same as the Sub DB main switch?
Thanks Chaps...
Sorry, I've given the wrong info already. 63A breaker supplying new sub board with 80A main switch.
Put a 63A contactor in then. probably around the same price anyway for a 20A or 63A 4pole contactor.
Edit: I didn't insert the skim link...you can get a 63A 4pole contactor for around ÂŁ25-ÂŁ30.
As above you need to know your load types IE resistive/inductive AC1/AC3 respective, the price different can be 2-3 times but get the wrong contactor and it may be damaged when operating under load. If in doubt or you have a high Inductive nature to the loads then fit a 30kw AC3 contactor with a coil rating of your choice dependent on the control voltage.
Clearly, the 'safe' thing to do is to size the contactor to the rating of the OCPD of the distribution circuit. This is probably the pragmatic thing to do if the additional cost for a higher rated contactor is small.
However, if the sole purpose of the board is to supply the kitchen ventilation system, which comprises several known fixed loads, I would not think it wrong to size according to the actual load current. If there is the possibility of overload, one could consider rating to the sum of the OCPDs in the board, especially if there is no possibility of adding more ways.
That's Where my confusion was coming in, I know the load, etc So was initially planning to size the contactor to that, But with it being a commercial kitchen the chance of someone adding a fairly high load item of equipment is always a threat.
So I've sized it to the OCPD. As you say, To be safe.
Being a fire alarm interlock do you need to make this a fail safe system?
Something like Spoon's suggestion above but with an undervoltage release rather than a shunt maybe?
Personally I'm not keen on contractors being installed such that they are permanently energised except when an alarm de-energises them, you don't know what may happen to cause it to stick in place and not find out until it is required to operate in an emergency
You won't get any real fail safe solutions here, that's why fire alarms and there auxillary operations are checked on a documented regular basis, only way to provide a better safety option would be fitting redundancy into the design so if one item fails then hopefully a second provides the same action to disconnect the supply. If this is for fire safety then a discussion with building control and the fire service may require a more robust solution, a simple fault been pulled through the contactor could weld it closed without anyone noticing hence the need for regular testing.
From my installation, but not alarm design, experience I would have thought that individual interfaces connected to the fire alarm system controlling the extraction units would have been the usual choice.
Seems a bit clunky to isolate the whole db, including any future additions, via contactor when specific items are required to be operated.
The OP states "I have a sub DB that need the supply isolating when a fire is detected (Commercial Kitchen)"
I presume that the sub DB is purely for the kitchen so the OP wants the whole DB isolating. Any additions to the DB should also be for the kitchen if that is the case.