Morning all,
Possibly a simple question But a mix of doctor prescribed medication and post Wembley joy have left my brain elsewhere.

I have a sub DB that needs the supply isolating if a fire is detected (commercial Kitchen) So The 3 phase supply for this DB needs a 4P contactor. Do I size the contactor to the current load of the sub board(10A) so Say a 20A contactor.
Or do I need to size the contactor to 63A same as the Sub DB main switch?

Thanks Chaps...
 
Thanks for the additional replies.
I hadn't even considered a shunt trip, It would've been a good idea, But a contactor has already been agreed with the client now. I guess its a bit 6 and two 3's, Possibly just a bit more work involved in the contactor.
All the loads are 3 phase, So we'll need the neutral switching.

Andy78 - Completely agree, Our usual way of dealing with this would be to interface the required vent units and isolate them alone. However, Due to the nature of the Building and System already installed that isn't possible. But The sub DB will be clearly labelled showing that in the event of a fire the supply to this DB will automatically isolate.
 
I would be looking at swapping out the Sub main main switch with an MCCB if possible and fitting a trip unit to it that runs through the Aux' of the fire alarm, this would be a similar cost but takes the contactor out of the loop.

Going down this road would require an extention box and the busbar kit to change over and usually comes complete (confirm with supplier), the aux trip will need to be specified on order.
 
Last edited by a moderator:
As davesparks has already posted, you might want to consider a undervoltage trip. Would be safer than a shunt trip in this case, from a fail-safe point of view. I suppose it depends on the fire alarm system.
 
All the loads are 3 phase, So we'll need the neutral switching.

I'm not sure why one follows from the other - a 3-phase motor load might not even have a neutral, although if it does say for control circuits any switching must be early-make late-break. If this were a manual isolator, it wouldn't necessarily switch the neutral. Is there a requirement for this?
 

Reply to Sizing a Contactor. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top