Hi Guys,

How do you know what size of earth wire to use from the bango to earth terminal in a DB, when using say:

25mm 4-core swa sub main feeding a DB. (L1, l2 l3 and neutral, armour used as cpc).

I would gland, with a bango and choose a size half of the phase size, so 16mm earth lead i would use. Is this ok, or OTT!?

so if 4mm2 armoured is used, I would use a fly lead of 2.5mm earth? Cant be wrong can it?

Cheers guys
 
Hi Platty,

The situation I had in mind, is when using armoured cable say 3 core for SP+E, or 5 core for TP+N+E, or 4 core for TP+E, it follows your cpc will be the same size as the line conductors as it is one of the cores, so this bit is straight forward.

Are you saying the banjo earth tail in this case has got to be the same size as the cpc ? or S/2 or by adiabatic ?, again this is when the armour is not used as the cpc, but is still required to be earthed, or is the exposed conductive part just extraneous as I cannot see a definite reg relating to this.

I was just asking out of interest, as the information seems a bit vague, I have seen earth tails in 2.5mm and in 4mm etc. , connected to the banjos, although I never took that much notice of what size the cpc/line conductors were, and whenever I have fitted them I have just used the same size as the cpc.

Any info./clarification welcome

All exposed conductive parts require connection via a CPC, if using the tables then the cpc is based on the line to which the cpc serves. the alternative is to use the adiabatic.

Regards Chris
 
Hi Platty,

The situation I had in mind, is when using armoured cable say 3 core for SP+E, or 5 core for TP+N+E, or 4 core for TP+E, it follows your cpc will be the same size as the line conductors as it is one of the cores, so this bit is straight forward.

Are you saying the banjo earth tail in this case has got to be the same size as the cpc ? or S/2 or by adiabatic ?, again this is when the armour is not used as the cpc, but is still required to be earthed, or is the exposed conductive part just extraneous as I cannot see a definite reg relating to this.

I was just asking out of interest, as the information seems a bit vague, I have seen earth tails in 2.5mm and in 4mm etc. , connected to the banjos, although I never took that much notice of what size the cpc/line conductors were, and whenever I have fitted them I have just used the same size as the cpc.

Any info./clarification welcome

Suggest you look at this link that was posted by Spinlondon in the stickyrelating to use of SWA as your CPC

steel wire armour as the earth conductor
 
Thanks for the link E54,

Most of the info. in that link refers mainly to using the armouring as the cpc or as a partial cpc (if undersized).

I was asking about the situation when the armourings were not used as the cpc, when a seperate core was used, but I suppose it is good practice to use the same csa for the banjo in this case, neglecting the fact that the brass gland will also act as a connection, although this may be unreliable due to paint etc. as GN8 says virtually nothing except it should be earthed.

I did not mean to hijack the OP's post but just thought it was relevant, and I realised I did not know 100% the answer. but glad at the same time that I always used the same size.

thanks,
Spark68
 
Last edited:
Thanks for the link E54,

Most of the info. in that link refers mainly to using the armouring as the cpc or as a partial cpc (if undersized).

I was asking about the situation when the armourings were not used as the cpc, when a seperate core was used, but I suppose it is good practice to use the same csa for the banjo in this case, neglecting the fact that the brass gland will also act as a connection, although this may be unreliable due to paint etc. as GN8 says virtually nothing except it should be earthed.

I did not mean to hijack the OP's post but just thought it was relevant, and I realised I did not know 100% the answer. but glad at the same time that I always used the same size.

thanks,
Spark68

Well the armor is classed as an exposed conductive part. So even when not used as a cpc, it still requires connection to earth via a cpc at the supply end. The cpc or fly lead needs to meet table 54.7 or use the adiabatic.

Lets assume the armour is of a sufficient size, 16mm 4 core, now we have two choices, use a 16 mm fly lead based on the line conductor or use the adiabatic to determine the size. Although the armour may be equivalent to say 16mm of copper the adiabatic may suggest 4 mm is fine so then a 4mm fly lead may be installed.

Dependent upon situation there is also the limitations as per 543.1.1, though unlikely in this instance.

Regards Chris
 
Last edited:
Hi Platty,

The situation I had in mind, is when using armoured cable say 3 core for SP+E, or 5 core for TP+N+E, or 4 core for TP+E, it follows your cpc will be the same size as the line conductors as it is one of the cores, so this bit is straight forward.

Are you saying the banjo earth tail in this case has got to be the same size as the cpc ? or S/2 or by adiabatic ?, again this is when the armour is not used as the cpc, but is still required to be earthed, or is the exposed conductive part just extraneous as I cannot see a definite reg relating to this.

I was just asking out of interest, as the information seems a bit vague, I have seen earth tails in 2.5mm and in 4mm etc. , connected to the banjos, although I never took that much notice of what size the cpc/line conductors were, and whenever I have fitted them I have just used the same size as the cpc.

Any info./clarification welcome
The CPC connects the exposed conductive parts to the MET so whatever the CPC size if you use the same size fly lead to connect to the Armour then you can't go wrong. Remember if there is an earth fault and the armour becomes live the fly lead needs to carry the fault current just like any other CPC
Taking it to the extreme a 120mm 4 core sub feeder with a separate 70mm cpc and the banjo fly lead is 1.5mm I don't think so.
As a general rule of thumb if the flylead = the cpc and the cpc is sized correctly then no problem
 

Reply to Sizing bango earth fly lead in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
643
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top