U
Unswitched
Hi Guys,
How do you know what size of earth wire to use from the bango to earth terminal in a DB, when using say:
25mm 4-core swa sub main feeding a DB. (L1, l2 l3 and neutral, armour used as cpc).
I would gland, with a bango and choose a size half of the phase size, so 16mm earth lead i would use. Is this ok, or OTT!?
so if 4mm2 armoured is used, I would use a fly lead of 2.5mm earth? Cant be wrong can it?
Cheers guys
543.1.4 says when not using adiabatic equation to calculate then use table 54.7, table states where line conductor is equal to or less than 16mm then protective conductor should be the same size.
On a related topic, what size fly lead should be used when the swa ISN'T the cpc? i.e. when merely wanting to earth the armouring, and one of the cores is the cpc?
IMO the flylead should still be sized as if it was CPC, as it would be relied on to disconnect the circuit in the event of somebody damaging the SWA. I dont know if this a BS7671 requirement, but in my mind its good practice
If you were to not use the armour as the CPC and were to use a separate conductor run along side the SWA, how would you determine the CSA required?
OP using 25mm 4 core with SWA as CPC
so CPC = S/2 if same material but it isn't it is steel
So you need to check CSa of SWA is compliant IE equivalent to 16mm copper
Assuming SWA CSA is compliant then fly lead should be 25/2 = 12.5 mm
No 12.5 cable so in this case 16mm copper fly lead is BS7671 compliant.
for 4mm with SWA as CPC fly lead 4mm is SWa compliant
for 4mm with core as CPC it is already 4mm so fly lead 4mm
Hi,
I have just been looking through GN8, GN8 9.3.5 and it says where the amouring is not used as a cpc it becomes an exposed conductive part (which requires earthing), but does not give any details as regards the banjo cpc/earth tail sizing.
Looking at GN8 table 8.1 supplementary bonding for exposed conductive parts give the usual 'where not protected mechanically min 4mm' etc.
The situation is not helped by GN8 not up to 17th ed. (this is the latest version).
I hear what other posters are saying re: sizing the same as cpc, but can anybody point to the relevant regs and guidance on this point ?, as I assumed (rightly or wrongly) the banjo tail would be 4mm, again when the armouring is not used as a cpc, for example where glanding the armoured cable into say a metal DB or metal Isolator etc.
TIA
If you are NOT using the Armour as the CPC then you must be using a separate CPC that must be sized correctly
It follows that the Armour is an exposed part of the circuit and must be connected to earth by a CPC so the banjo fly lead = same size as the CPC what ever that is. EG: CPC = 2.5 fly lead 2.5, CPC 4mm fly lead 4mm and so on To size the CPC use Adiabatic formula or table in Regs
Hi Platty,
The situation I had in mind, is when using armoured cable say 3 core for SP+E, or 5 core for TP+N+E, or 4 core for TP+E, it follows your cpc will be the same size as the line conductors as it is one of the cores, so this bit is straight forward.
Are you saying the banjo earth tail in this case has got to be the same size as the cpc ? or S/2 or by adiabatic ?, again this is when the armour is not used as the cpc, but is still required to be earthed, or is the exposed conductive part just extraneous as I cannot see a definite reg relating to this.
I was just asking out of interest, as the information seems a bit vague, I have seen earth tails in 2.5mm and in 4mm etc. , connected to the banjos, although I never took that much notice of what size the cpc/line conductors were, and whenever I have fitted them I have just used the same size as the cpc.
Any info./clarification welcome
Hi Platty,
All exposed conductive parts require connection via a CPC, if using the tables then the cpc is based on the line to which the cpc serves. the alternative is to use the adiabatic.
Regards Chris
Hi Platty,
Suggest you look at this link that was posted by Spinlondon in the stickyrelating to use of SWA as your CPC
steel wire armour as the earth conductor
Thanks for the link E54,
Most of the info. in that link refers mainly to using the armouring as the cpc or as a partial cpc (if undersized).
I was asking about the situation when the armourings were not used as the cpc, when a seperate core was used, but I suppose it is good practice to use the same csa for the banjo in this case, neglecting the fact that the brass gland will also act as a connection, although this may be unreliable due to paint etc. as GN8 says virtually nothing except it should be earthed.
I did not mean to hijack the OP's post but just thought it was relevant, and I realised I did not know 100% the answer. but glad at the same time that I always used the same size.
thanks,
Spark68
thanks,
Spark68
Well the armor is classed as an exposed conductive part. So even when not used as a cpc, it still requires connection to earth via a cpc at the supply end. The cpc or fly lead needs to meet table 54.7 or use the adiabatic.
Lets assume the armour is of a sufficient size, 16mm 4 core, now we have two choices, use a 16 mm fly lead based on the line conductor or use the adiabatic to determine the size. Although the armour may be equivalent to say 16mm of copper the adiabatic may suggest 4 mm is fine so then a 4mm fly lead may be installed.
Dependent upon situation there is also the limitations as per 543.1.1, though unlikely in this instance.
Regards Chris
Hi Platty,
The CPC connects the exposed conductive parts to the MET so whatever the CPC size if you use the same size fly lead to connect to the Armour then you can't go wrong. Remember if there is an earth fault and the armour becomes live the fly lead needs to carry the fault current just like any other CPC
Taking it to the extreme a 120mm 4 core sub feeder with a separate 70mm cpc and the banjo fly lead is 1.5mm I don't think so.
As a general rule of thumb if the flylead = the cpc and the cpc is sized correctly then no problem
Sizing bango earth fly lead
Australia
Unswitched,
scotsparky,