check out page 49 on GN8. Installaition serving more than one building. It states that "the application of the regulation where it serves a number of buildings it can result in the csa of the main equipotential bonding conductors being required to be grater than the associated live conductors of the distribution circuit suppling that building, Particuarlly where PME conditions apply" . It also shows diagramms of buldings being supplied from the main building Of 16mm live conductors with a 25mm combined cpc and bonding conductor for tns and similar diagramm for pme , 16mm supply conductors and a 35mm combined cpc and bonding conductor.
We find most places we go to, bonding conductors to be sized on the consumers distribution circuit, which is wrong.