After a couple of bonding conductor questions I had I've started a new post for this so it's more specific.

I have a TN-C-S installation, at least 70mm line and neutral at the incomer, feeding a main distribution board which feeds 8 x 3 phase boards around a site. We are installing a 16mm SWA from this dis board to a new 3 phase board in a new building. Using the armour sheath as main earth for this board.

I have decided after my other post that the main bonding for gas and electric entering the new building will be run as a single separate continuous cable and tied to the SWA, but I am having a problem sizing it up.

First question is to check that the bond for these 2 services does need linking all the way back to the MET at the origin in the main building 50m away, and not just to the main earth in the new board in the new building (1m away).

If I went by the book it seems I should be going by the size of the incoming neutral of the supply in the main building, and the 16mm feed we're putting in seems irrelevant. So if our neutral at the supply is 70mm, we'd end up running a 25mm bond alongside our new 16mm feed. Seems over the top.

You can see my confusion - the board and feed that's going in is a separate building with this feed from the main building. In essence the new building is it's own equipotential zone and it makes more sense to me to bond the services in there to the MET in there, and not link back to the MET at the origin in another building.

Could someone please clarify this for me as it's driving me nuts, it's such a simple setup but I'm obviously missing the trick here. I've drawn a pretty picture too! :confused: [ElectriciansForums.net] Sizing bonding for subboard
 
Distance is about 5 metres from the main building wall - wall but about 40m from the main supply. It's a permanent structure so I don't want to get start arguments about exporting PME :)
 

Reply to Sizing bonding for subboard in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
494

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top