sizing meter tails and switch fuse discrimination | on ElectriciansForums

Discuss sizing meter tails and switch fuse discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

J

jase31

DNO has upgraded service fuse from 30a to 60a, they do not want to go any higher due to the main feed cable.

CU is 4-5m away, connected via switchfuse. Should 16mm or 2mm tails be used, OSG recommend 25mm but seems to assume a 100a supply.

With a 60a head, what size switchfuse should be used for discrimination?
 
Last edited by a moderator:
The DNO fuse is protecting their equipment.
Don't worry about discrimination with their fuse.

With a 60a head, I cant really see the need for a customer switch fuse for 25mm tails that are 4-5m long, but I understand that DNO insist on a switchfuse over 3m. What fuse should be used? 60A
 
hi spin london, when sizing cables 25mm and above what do you use as Mv/A/m there is 3 options, isit normal too use z option????

Upto 35mm, I continue to use the resistive (r) component for calculating the VD. By moving to the impedance (z) component you will end up with a pessimistically large conductor size.

Going above 35mm and bringing reactance & impedance in to play makes it all a bit more complicated as power factors (if known) and temperature corrections come into play.

Have a read from page 312 (new green book) onwards (appendix 4).
 
Last edited by a moderator:

Reply to sizing meter tails and switch fuse discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
716
  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
719

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top