Sizing MPCB | on ElectriciansForums
Discuss Sizing MPCB in the Talk Electrician area at ElectriciansForums.net
New Zealand
Hi guys, just making sure that I'll be choosing the right size of MPCB, motor connected in star with current 3.32A, would a MPCB rated at 4A - 6.3A be good enough? Thanks!
that would be fine if your also using a contactor and overload relay that is set to FLC of motor.
but if that is the only device protecting the motor from overload then as @SheffSimon says above, get the correct matched rating (nameplate of motor, not actual current measured) or the motor will burn out before the breaker trips.
Reply to Sizing MPCB in the Talk Electrician area at ElectriciansForums.net
Don't worry about the 4A fuse, it's a Keston boiler, it'll be dead by the time you've found one and it's been delivered.
davesparks
R
Radiator size Hi. Currently have 3 small double radiators (500x600) in our open plan living room/kitchen diner. Would like to change them for...
robcharlton
R