Hi, am looking to upgrade my electrical shower from 9.5 to 10.5kw and am unsure if my cable is upto the job as its 6mm attached to a 40A fuse. The length of the run from fusebox to shower is approx 12-15m so I am trying to check if its a viable project as I have no desire to upgrade the cable to 10mm given the route.
If there is a formula for this calculation then that would be a big help.
Thanks
 
What do the manufacturers instructions say? I would expect they would say 10mm cable as 10.5kW (45.6Amps) and the instructions would/should override any calculations.

I really depends on how the cable is installed - for example from the IET Wiring Regulations, if run in insulated stud wall its current carrying capacity (CCC) could be as low as 27.5A . Enclosed in a plastered wall - 32A so you see way below what a 10.5kW shower would draw.
 