H

havoone

I did the 2382 last year and during the coarse the lecturer told us that in NEW domestic dwellings the live tails would now have to be 25mm. I cant seem to find where in the regs he came up with this but I think it was associated with chapter 54/earthing, and some cross referencing. any idea ? thanks.
 
Meter tails are part of the consumers installation and are to be provided by the installer. Meter tails must be sheathed and insulated or if insulated only must be enclosed in trunking or conduit. Meter tails must be 25mm. Where the meter tails are protected against fault current by the main fuse the installation method, maximum length and minimum cross sectional area must meet the distributors requirements. OSG p17.
 

Reply to sizing tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
375
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
943
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2 3 4
Replies
47
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top