Hello fellas. Had the dno trying to tell me that a 19 ohm ze reading on a tns system was ok to leave energised? Seriously? Can someone please explain to me how that is ok?
 
So...
You didn't bother to get yersen a Ze first... before doing your stuff...?

See how now your responsible for getting it sorted for em...?

I’m only responsible for getting the dno out to sort their problem. Once it’s handed over to them it’s out of my hands. That’s how I see it anyway
 
Before the universal reliance on Rcds,if the same situation arose on a system in the past ,that high reading may have led to getting advice to provide Rcd protection until its sorted,same as now

Perhaps its the workplace perception of the potential danger that is changing as the system protections gets better
 
Before the universal reliance on Rcds,if the same situation arose on a system in the past ,that high reading may have led to getting advice to provide Rcd protection until its sorted,same as now

Perhaps its the workplace perception of the potential danger that is changing as the system protections gets better
But then do we not risk an over reliance on RCDs and installation standards will drop where other protective devices are concerned?

Don't worry about the R1+R2 being a little high, just chuck it on an RCD...
 

Reply to Sky high ze reading in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
402
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top