Hello fellas. Had the dno trying to tell me that a 19 ohm ze reading on a tns system was ok to leave energised? Seriously? Can someone please explain to me how that is ok?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Sky high ze reading in the UK Electrical Forum area at ElectriciansForums.net
So...
You didn't bother to get yersen a Ze first... before doing your stuff...?
See how now your responsible for getting it sorted for em...?
I’m only responsible for getting the dno out to sort their problem. Once it’s handed over to them it’s out of my hands. That’s how I see it anyway
But then do we not risk an over reliance on RCDs and installation standards will drop where other protective devices are concerned?Before the universal reliance on Rcds,if the same situation arose on a system in the past ,that high reading may have led to getting advice to provide Rcd protection until its sorted,same as now
Perhaps its the workplace perception of the potential danger that is changing as the system protections gets better