Slightly high Zs on large ring circuit | on ElectriciansForums

Discuss Slightly high Zs on large ring circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

PB1

Hi all, I did a PIR yesterday at a largeish house (150m2). there is only 1 ring final circuit for all house sockets. Zs was 1.25ohms, vs 1.16 permitted maximum value. there is an RCD so additional protection in theory although the RCD did not disconnect at 5x 30 ma test. I will obviously recommend replacing the RCD, but wondered what to say if anything about the size of the ring as the length of the cable is presumably the reason that the EFLI is too high. Given that RCDs do fail sometimes the circuit will not meet the disconnection time for the B32 breaker that is protecting it. Any advice greatfully appreciated.
 
If the RFC was additionally protected by a tested and fully functional 30mA RCD the maximum Zs for the final circuit would be 1667 Ohms (BRB, Table 41.5), so your measured Zs of 1.25 Ohms easily complies with BS7671 in this respect. On a TN system in most cases the absence of fully functional additional RCD protection would warrant a PIR Code 4, however if the RCD also covers final circuits a special location (e.g. bath or shower) and the bonding requirements of BRB 701.415.2 are not satisfied, or the supply of mobile equipment outdoors can reasonably be expected, a PIR Code 2 would be appropriate. You should recommend to your customer that the RFC should be split in to 2 or more smaller final circuits, ring or radial as appropriate. The guidance from the OSG Appendix 8.2 is that an A1 RFC should not serve a floor area greater than 100m[SUP]2[/SUP], the reasoning behind this is that the greater the floor area served by a RFC the greater the chance of unbalanced current distribution of the total load in each leg of the RFC. Depending on your assessment of likely distribution of high current using appliances on the RFC and degree to which BRB 433.1.5 is infringed, this may warrant a PIR Code 2 or 4 accordingly.
 
Last edited by a moderator:

Reply to Slightly high Zs on large ring circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top