Hi all, I did a PIR yesterday at a largeish house (150m2). there is only 1 ring final circuit for all house sockets. Zs was 1.25ohms, vs 1.16 permitted maximum value. there is an RCD so additional protection in theory although the RCD did not disconnect at 5x 30 ma test. I will obviously recommend replacing the RCD, but wondered what to say if anything about the size of the ring as the length of the cable is presumably the reason that the EFLI is too high. Given that RCDs do fail sometimes the circuit will not meet the disconnection time for the B32 breaker that is protecting it. Any advice greatfully appreciated.