what mm2 can I get away with on a 40m run between a tripower17000 and the metering point.
The Instructions states:
6 mm2 up to 31m
8 mm2 up to 41m
10 mm2 up to 52m
16 mm2 up to 83m
It states the resistance is not allowed to be above 1 Ohm and the loss is not above 1%
otherwise the inverter might trip at peak load.
We messured 0.6 Ohm on a 40m run of 4 mm2.
Has anybody got experience with this,
What would you recommend?
Regards
germ