Can anyone tell me what the minimum dBA should be for a domestic smoke alarm system at the bed head?
 
It would be really useful when replying to such a question to provide a reference to the answer so that the questioners can be certain of the authority of the answer.
 
BS5839 as summarised by ttsfire.co.uk states:
Alarm Sound Levels

It is essential that, whenever any of the smoke alarms in the dwelling detects a fire, the sound level of the alarm (from either that smoke alarm or other smoke alarms interconnected with it) is sufficient to wake up at least the adult members of the household. The sound level in any bedroom is likely to be satisfactory if there is a smoke alarm in the bedroom, interconnected to all other smoke alarms in the dwelling. However, if this is not the case, the nearest interconnected smoke alarm to the bedroom, capable of sounding an alarm whenever fire is detected anywhere in the dwelling, should not be further than 3 m from the bedroom door.
In some dwellings, such as flats, maisonettes and houses in multiple occupation, doors to rooms may be fire doors, which tend to attenuate the sound from smoke alarms more than normal, domestic doors. In these cases, great care should be taken to ensure that the sound level in bedrooms is sufficient. In some houses in multiple occupation, the local authority may demand that the sound level at the bedheads in some or all bedrooms is 75dB(A) when the bedroom doors are closed. This should be determined before finalising the number of smoke alarms required, because 75dB(A) is unlikely to be produced at the bedhead unless there is a smoke alarm within the bedroom.
If occupants suffer from severe hearing impairment, BS 5839 : Part 6 recommends that special alarm devices, such as high intensity beacons and vibrating pillow or mattress pads, be provided.
 

Reply to Smoke Alarm minimum dBA in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
823
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
906

Similar threads

  • Question
Personally I won't do fixed price work unless there is a clear spec for the job including things like smokes, data, TV whatever else the customer...
Replies
3
Views
773
These keypads are obsolete and replacements are hard to find, I've replaced loads now with failing displays. Sounds like something isn't...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top