O

Octopus

Hi,

I've been asked if I want to quote for installing fire/smoke/heat alarms in a local community hall which has several rooms and quite a high "domed" ceiling in the main room.

Having not done anything like this before would any members like to give me their thoughts/and/or guidance on such a solution.....


Thanks
 
Hi,

I've been asked if I want to quote for installing fire/smoke/heat alarms in a local community hall which has several rooms and quite a high "domed" ceiling in the main room.

Having not done anything like this before would any members like to give me their thoughts/and/or guidance on such a solution.....


Thanks

Woah!

If it's a community hall - i.e. where public gather to do activities, etc - then it is first and foremost subject to the Regulatory Reform (Fire Safety) Order:2005, and MUST have a current valid fire risk assessment in place.

For you, this means a minimum specification will have been identified and set for any electronic fire detection (as well as for other fire measures, such as extinguishers, blankets, etc.).

Primarily, this means (and is most likely the case) that you will have a document, signed off by an expert (hopefully) who will have defined the grade and category to which the fire detection needs to comply, and to be honest, if this isn't in place, I'd throw it back at whoever asked you, and tell them to comply with the law first - that risk assessment is a LEGAL requirement.

Most likely, and without seeing the property, you'll be looking at a system which needs to comply with BS5839-1:2008. In other words, not smoke detectors in the sense of what you'd install at home. In all probability if the building is only occupied part time, and isn't attached, or posing risk to other premises, the requirement will probably be for an L2 or L3 system design.

Now, you've mentioned high domed ceilings too - those are subject to different spacing rules over the standard spacing set out - normally by reducing the distance by an amount for every so many degrees of pitch the ceiling rises. Any obstruction on the ceiling which is over 10% of the height of the room at any point will also need to be considered.

Given all this - and with all respect, it isn't something you want to "play" with - the penalties for getting it wrong hurt, and include prison if it all goes horribly wrong. Get a professional in to at least design the system (and if necessary carry out the risk assessment) - and play safe. If you're looking for a good fire company in Surrey......by the way :)

As Alarm Man says - collaboration is probably your best bet - get someone with experience..... to at least do the design, and commissioning....and guide you on install if necessary.
 
Hi,

I've been asked if I want to quote for installing fire/smoke/heat alarms in a local community hall which has several rooms and quite a high "domed" ceiling in the main room.

Having not done anything like this before would any members like to give me their thoughts/and/or guidance on such a solution.....


Thanks

Woah!

If it's a community hall - i.e. where public gather to do activities, etc - then it is first and foremost subject to the Regulatory Reform (Fire Safety) Order:2005, and MUST have a current valid fire risk assessment in place.

For you, this means a minimum specification will have been identified and set for any electronic fire detection (as well as for other fire measures, such as extinguishers, blankets, etc.).

Primarily, this means (and is most likely the case) that you will have a document, signed off by an expert (hopefully) who will have defined the grade and category to which the fire detection needs to comply, and to be honest, if this isn't in place, I'd throw it back at whoever asked you, and tell them to comply with the law first - that risk assessment is a LEGAL requirement.

Most likely, and without seeing the property, you'll be looking at a system which needs to comply with BS5839-1:2008. In other words, not smoke detectors in the sense of what you'd install at home. In all probability if the building is only occupied part time, and isn't attached, or posing risk to other premises, the requirement will probably be for an L2 or L3 system design.

Now, you've mentioned high domed ceilings too - those are subject to different spacing rules over the standard spacing set out - normally by reducing the distance by an amount for every so many degrees of pitch the ceiling rises. Any obstruction on the ceiling which is over 10% of the height of the room at any point will also need to be considered.

Given all this - and with all respect, it isn't something you want to "play" with - the penalties for getting it wrong hurt, and include prison if it all goes horribly wrong. Get a professional in to at least design the system (and if necessary carry out the risk assessment) - and play safe. If you're looking for a good fire company in Surrey......by the way :)

As Alarm Man says - collaboration is probably your best bet - get someone with experience..... to at least do the design, and commissioning....and guide you on install if necessary.
 
So how much would it cost to design a system bill??? Rough idea,and do assessment?

Caps off now.

Realistically, risk assessment we do from ÂŁ250 plus VAT - which is fully BS9999 compliant, and include a written report, fire action plan, and associated material. A typical assessment will take up to four hours on site plus compilation time for the report (plus, it passes some risk in fire safety from you to us).

System design - depends on size and complexity of requirements, number of site visits needed, meetings to attend, design time, and so on - but for a small system such as described above, would be probably around the ÂŁ200 plus VAT mark - and again, passes risk in design from you to us, which is probably the critical bit, aside from ongoing maintenance records - well, commissioning is important too.

Again - prices are guide, negotiable depending on scope of it all, and a better idea of actual requirements :)
 
Woah!

If it's a community hall - i.e. where public gather to do activities, etc - then it is first and foremost subject to the Regulatory Reform (Fire Safety) Order:2005, and MUST have a current valid fire risk assessment in place.

For you, this means a minimum specification will have been identified and set for any electronic fire detection (as well as for other fire measures, such as extinguishers, blankets, etc.).

Primarily, this means (and is most likely the case) that you will have a document, signed off by an expert (hopefully) who will have defined the grade and category to which the fire detection needs to comply, and to be honest, if this isn't in place, I'd throw it back at whoever asked you, and tell them to comply with the law first - that risk assessment is a LEGAL requirement.

Most likely, and without seeing the property, you'll be looking at a system which needs to comply with BS5839-1:2008. In other words, not smoke detectors in the sense of what you'd install at home. In all probability if the building is only occupied part time, and isn't attached, or posing risk to other premises, the requirement will probably be for an L2 or L3 system design.

Now, you've mentioned high domed ceilings too - those are subject to different spacing rules over the standard spacing set out - normally by reducing the distance by an amount for every so many degrees of pitch the ceiling rises. Any obstruction on the ceiling which is over 10% of the height of the room at any point will also need to be considered.

Given all this - and with all respect, it isn't something you want to "play" with - the penalties for getting it wrong hurt, and include prison if it all goes horribly wrong. Get a professional in to at least design the system (and if necessary carry out the risk assessment) - and play safe. If you're looking for a good fire company in Surrey......by the way :)

As Alarm Man says - collaboration is probably your best bet - get someone with experience..... to at least do the design, and commissioning....and guide you on install if necessary.

Hes Back!!! :)
 
Realistically, risk assessment we do from ÂŁ250 plus VAT - which is fully BS9999 compliant, and include a written report, fire action plan, and associated material. A typical assessment will take up to four hours on site plus compilation time for the report (plus, it passes some risk in fire safety from you to us).

System design - depends on size and complexity of requirements, number of site visits needed, meetings to attend, design time, and so on - but for a small system such as described above, would be probably around the ÂŁ200 plus VAT mark - and again, passes risk in design from you to us, which is probably the critical bit, aside from ongoing maintenance records - well, commissioning is important too.

Again - prices are guide, negotiable depending on scope of it all, and a better idea of actual requirements :)

Would you be interested in working with me on this?
 
if ou rang the fire brigade, would they do survey for free...??? i know they can do some stuff

The fire service will not design a fire alarm system or take responsibility for the safety of the building. They will ensure that escape routes are adequate for the flc of people that could be in the building at the time of an evacuation, the amount, type and placement of extinguishers and also the storage of flammable/toxic vapour releasing fumes, fire doors. They do a great job but not to the extent of designing a fire detection system.
 

Reply to Smoke alarms for community hall in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
689
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
657

Similar threads

  • Question
Personally I won't do fixed price work unless there is a clear spec for the job including things like smokes, data, TV whatever else the customer...
Replies
3
Views
760
  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
660

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top