Under BS5839-part 6 your dwelling would be classed as a "Grade D" system.
There is a conflict that some people come across that is BS 5839-1 says that for reasons of electrical safety, the mains supply to all parts of the fire alarm system should not be supplied via an isolating protective device (such as a circuit-breaker), BS 5839-6 on the other hand, says that the circuit serving the fire detection and alarm system should preferably not be protected by any residual current device (RCD). Which is right?
Dedicated circuits are required for Grades A, Band C systems, and BS5839- 1 systems, so the use of an RCD is not allowed. With the introduction of the 17th Edition of BS 7671 lEE Wiring Regulations, all new dwellings may be required to have RCD protection. Where "Grade D" smoke alarms are supplied from a frequently used lighting circuit, it is likely that, by default, this will be provided with an RCD unit. Grade E systems cannot be connection via an RCD. Now new and altered domestic installations, which include fire systems, will be required to have 30mA RCD protection throughout.
On a side note "Grade C, D, E" do not require fire resistance cable for them to be wired in these grades of system need only to be provided with general cables such as T&E, which are suitable for the voltage and current being used by the system. Only Grades A and B require fire-resistant cables.
So to sum up, you can wire it in T&E and because of the type of building it does not require local isolation like a spur.