edward cooper
I recently got a call to my uncles club because lights had gone down in the ladies. neutral had burnt out but mcb (from 1981) never operated. so when he called me I said probably loose connection and arched and burn't out as it was right by the terminal block. Turns out her replaced the fitting six months prior.
Said i would come have look as I have only just completed my 2330 and regs courses.
Grabbed my meter few tools and though i might as well check the circuit while i am there.
Took the cover off the board was faced with 4 lighting breakers 15, 10, 10, 10 amp with at least 3 to 5 lighting circuits on each then running 1mm twin and earth looked at the rest of the board and discovered this 12 way board was running about 35 circuits. No wonder it did not operate
so i asked for his last periodic results to which was well i know i should have them but we dont. i then explained the need for them and also explained that i think if he were to have it done now that i think the visiting spark would probably condem his system.
So i am now standing there thinking i now know why he never called in registered spark as i am not starting 2391 till september.
What advice do you all have.
I think if i was registered I would condem it till it had at least a board change all circuits seperated and full periodic completed and faults rectified.
lookforward to replies
Said i would come have look as I have only just completed my 2330 and regs courses.
Grabbed my meter few tools and though i might as well check the circuit while i am there.
Took the cover off the board was faced with 4 lighting breakers 15, 10, 10, 10 amp with at least 3 to 5 lighting circuits on each then running 1mm twin and earth looked at the rest of the board and discovered this 12 way board was running about 35 circuits. No wonder it did not operate
so i asked for his last periodic results to which was well i know i should have them but we dont. i then explained the need for them and also explained that i think if he were to have it done now that i think the visiting spark would probably condem his system.
So i am now standing there thinking i now know why he never called in registered spark as i am not starting 2391 till september.
What advice do you all have.
I think if i was registered I would condem it till it had at least a board change all circuits seperated and full periodic completed and faults rectified.
lookforward to replies