Socket earthing yeah or neah | on ElectriciansForums

Discuss Socket earthing yeah or neah in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

Darkwood

Doing a pir at mo and on checking the sockets (ring) noticed the earths had been terminated as a pair into the backbox with a 1.5mm tail to socket, ive knocked this as i see it as a weak link and requires the pair to terminate onto socket with tail link to the back box. Whats your feed back?
 
CPC's to primary means of earthing which is the earth terminals on the socket.

No need to earth the back box as it not an extraneous conductive part and them there two M3.5's cover it anyways. I always do, though.

Code 4 ?
 
I was expressing the manner in which the socket got an earth and that the ring earth didnt run through the socket, and back boxes do need earthing but if they have at least one fixed thread on them then you can rely on the 3.5 screw to achieve this, but its looked on as good practice to earth it anyway.
 
Guys tell me if I am getting it wrong here but I served my time in the 14th edition yes I know and running a seperate earth cable was not done as the containment system ie trunking and conduit were classed as "electricaly and mechanically sound" so you had no option but to put in a lead from the box earth terminal to the socket also if you wired in T&E you still had to put the lead in.Now this is where it gets interesting as some sparks would twist both earths and the lead and terminate it on the stud on the back box others would do the reverse. So why put the lead in ? well the whole idea was that when you took the screws out and pulled the socket back the socket still had to be earthed. So do you still have to put the link in with ref to the 17th
 
We are not supposed to remove the socket live,so the need for an extra earth to the back box would not arise
It does seem to be good practice,but not any sort of requirement, unless the earthing cant be maintained whilst live by dodgy movable lugs,hence the one fived lug quotes
 
both cpc into seperate earth terminals of socket (if there are two) not twisted, seperate earth sleeeving for each and addidional cpc to terminal in metal back box
 
The CPC's only need terminating into separate earths terminals on the sockets if the circuit has to incorporate high integrity earthing arrangements.

Must admit, good idea regardless though.

:)
 
It seems no-one has picked up on my original question, the point i was making was you cant run the earth ring through the backbox with a 1.5mm tail to the socket, the earth ring must go to the socket and the 1.5mm tail to the backbox if you fit one, i well aware of the regs with tailing backboxes but the point of my question was the manner in which a socket i came across had its earthing terminated. As i pulled the ring main for this in the PIR i just wanted your feedback.
 
It seems no-one has picked up on my original question, the point i was making was you cant run the earth ring through the backbox with a 1.5mm tail to the socket, the earth ring must go to the socket and the 1.5mm tail to the backbox if you fit one, i well aware of the regs with tailing backboxes but the point of my question was the manner in which a socket i came across had its earthing terminated. As i pulled the ring main for this in the PIR i just wanted your feedback.

That is correct as you say Darkwood. Cpc conductors from ring must be terminated at socket not back box. Then fly lead if required.

If i came accross sockets terminated like that whilst doing a PIR i would code 2 it and therefore PIR would be unsatisfactory.
 
what about 1leg in box 1leg in socket and a link between
seen this often
Cant argue with this one as it still has the ring earth going through the socket and have seen this a few times myself although not my preferred choice as damp in the wall would create a corroded terminal as ive also seen this many times.
 
Was R1+R2 ok? was Ze ok?
How can you give this a code anything? this was a pir you were doing, you can't give it an unsatisfactory report just because it doesn't measure up to your interpretation of good practice.
 
Was R1+R2 ok? was Ze ok?
How can you give this a code anything? this was a pir you were doing, you can't give it an unsatisfactory report just because it doesn't measure up to your interpretation of good practice.
Its not an interpretation of good practice its a weak link in the circuit as an example if a a short circuit occurs L/E on the ring main then it normally has 2 X 1.5mm paths to run the high current through until the fuse operates but as we know the standard practice of a ring is to front end with a 32amp mcb/rcbo which overates the cable but is allowed due the nature of load sharing around the ring. If you earth ring the backbox then tail the socket to earth it if the fault is on a item plugged into this socket then then the earth tail has to cope with the full fault current which is then shared when it joins the earth ring.
So in effect the fault path has to go through a undersized link which may not withstand the fault current in this case 1500amps, the solution is simple by just fitting 4mm links but i was putting the issue forward to see what others like yourself thought.
Ps this is only to the 16th so no rcd protection so only the time/current curve of the mcb can be relied on.
 
Last edited by a moderator:

Reply to Socket earthing yeah or neah in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
As you said in #9 get an electrician involved. The information you are giving is not clear as you do not understand what is being asked which...
Replies
10
Views
1K
Thanks Brian. I'll keep doing it then, no harm I suppose. I am lucky in that being DIY, I have the luxury of time when it comes to this kind of...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top