I was having a look at my cu the other day and noticed that someone had connected a double socket (socket is situated just below the cu) straight off the mcb, which includes the wiring of the final ring.

I'm unsure if this conforms with regs etc

We do actually use it for the intruder alarm but quite prepared to disconnect if it is unsafe.

3rd mcb from left
 

Attachments

  • CU.JPG
    CU.JPG
    367.8 KB · Views: 64
nothing wrong with it. it's just a unfused spur with 1 outlet, taken from the MCB ( as allowed in BS7671 app.15.) but should your alarm not be connected via an unswitched FCU?
 
Tels nailed it... don't treat your mcb as the supply point, treat it as a connection point just like a socket outlet, its perfectly fine to spur off a socket on the ring and the mcb is no different to doing as it is just a connection point along the ring final circuit.

Appendix 15 as already suggested is the best place to check.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
-
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
socket off the back of MCB
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
gazdkw82,
Last reply from
gazdkw82,
Replies
4
Views
91

Advert

Back
Top