Hi just a silly question but I have to ask this . On socket outlets which are for general use it says that they have to now be 20amp and rcd protected. Does that mean that 32amp socket outlets for general use have to be down graded ?
 
Think you getting reg 411.3.3 concering additional protection and the use of RCDs for socket outlets.

Section (i) of the reg tells us that a socket outlet for general use of ordinary persons and less than 20amps must have RCD protection with characteristics in reg 415.1

And mobile equipment for use out door not exceeding 32amps must also be RCD protected
 
Ok I think I get it . So socket outlets on a 32amp mcb and have rcd protection are ok as they are more thank 20 amps .
Is this because the disconnection times are higher with just the 32amp mcb and the rcb is just for added protection .
Thanks for your help.
 
Grae not sure what you saying but what it is not correct.

First have you a regs books ? If you have then read reg 411.3.3 Additional protection for socket outles are covered in this section

The regs says that sockets not exceeding 20amps must have RCD protection as I stated above, for ordinary persons and general use, so in a factory you could easily have a 32 amp socket not on RCD protection and still be good.

Higher disconnection times are used on distribution circuits not on final circuits
 
Either read the regs or get an electrician to look at your set up. By all means down rate the MCB’s, you’ll soon change them back.
Personally I think you’re on planet Spongle.
 
The OP is getting confused between the socket outlet (which in domestic situation is typically for 13A plugs and therefore is of type < 20A when applying the regs) and the OCPD for the circuit (typically 32A for such a circuit). The regs in this case are referring to the type of socket outlet, not the circuit it is on.
 
I have just done the 17th and maybe I need some down time ! But I'm having a problem with the wording maybe. When it talks about sockets not exceeding 20amps must have RCD protection.
 

Reply to socket outlets in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

Stick the socket in a large plastic wall box with hinge and padlock. Give customer letter with key...
2
Replies
17
Views
4K
Hi My first post here, so apologies for any mistakes. I think it will be DIY job with electrician sign off if required, but would like to do as...
Replies
0
Views
188

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top