I'd be asking why it was done that way in the first place?
Would that not be clear and obvious to you at the point of inspection as the OP found out
I know UNG raises the point that it's not bad workmanship but it just doesn't sit right; if it is there for a specific purpose then yes (S)FCU it as it removes the "Ohh a plug, just what I need for the roof decorations at Christmas.
Have you not been reading all the posts in this thread where the likely reason for the installation of sockets on the lighting circuit rather than FCU's has been mentioned and discussed
If it is there for a set purpose then give it a standard radial with standalone OCPD.
If it is there for lighting then why not connect it to the local lighting circuit putting a separate circuit with it's own OCPD would then have two circuits in one light switch again not codeable but probably presents a greater danger to a dabbling Mr DIY
As C3 does naff all to the end result of the EICR I see no harm in attaching a code to it. I know there are various softwares out there that give a CO (Comment Only) option but I refer to earlier; if it doesn't fail it then why not use what is already there?
A C3 is a code like it or not so a "Code C3 – Improvement recommended" what improvement are you going to recommend when you cant plug a lighting adaptor / driver into an FCU
I respect the opinions of my fellow peers and on most points, will take their advises and counter-arguments and constructive comments but I dunno, it doesn't sit with me, hence my approach, maybe it's just naivety with lack of real world experience, who knows
While it might not "sit with you" it is what it is, the real problem is we have to work with what the manufacturers supply which is genearlly all down to cost but also down to what Mr DIY can easily fit
What is engineering judgement to one person could be --------, -------s and baloney to the next but that is why I love this place; many minds coming together and debating basic stuff.
From a coding point of view there really isn't much to discuss but it does highlight what maybe an over zealous inspector that acts with a coding before considering why and whether there are any better or alternative solutions that could have been offered or installed

This is one of those situations where a coding may be called out and subsequently the quality of the EICR and inspector called into question
 
Last edited:
I know UNG raises the point that it's not bad workmanship but it just doesn't sit right; if it is there for a specific purpose then yes (S)FCU it as it removes the "Ohh a plug, just what I need for the roof decorations at Christmas. If it is there for a set purpose then give it a standard radial with standalone OCPD
I know what you are saying, because the sockets were installed for a certain intended purpose. But the truth is does it really matter? The position of the sockets alone is a limiting factor and so they are not likely to be used regularly for anything that is likely to overload the circuit.

Provided the circuit has been design and installed with the correct OCPD in place and working then the circuit is safe to use and doesn't present a danger.

So if Bob comes along with his 3kw fan heaters and decided to use the sockets, the OCPD will operate and protect the circuit from overload. If Bob plugs in his Christmas lights and the circuit remains energised then the lights are unlikely to be overloading the circuit. A simple label to state the intended use of the circuit or non-use of the circuit will advise against incorrect use. If the consumer decides to ignore this and continue to overload the circuit or attempt to bypass the OCPD then that's their idiocy and they will have to deal with the consequences.

We are electricians not bay sitters, our duty is to install safe systems to a standard guided by the BS7671 regs . We can't and shouldn't second guess every single possible scenario, just a little thought on the most likely ones.
 
People in the UK have a problem with mixing socket outlets and lighting on the same circuit, it isn't convention therefore it is wrong but it isn't.
Before AM2 the regs made a distinction between "lighting circuits" and "power circuits" in terms of cable selection in Table 52.3 where 1mm could be used for lights and according to Note 4 "associated small items of current-using equipment, such as a bathroom extractor fan", but you had to use 1.5mm for general power circuits.

Now in AM2 that has been dropped along with 'Note 4' which sort of makes sense, as you could have the absurd situation of stand alone smoke alarms having to be wired in 1.5mm but if fed off lights then 1mm was fine!

As I already said, I have no issue with sockets on light circuits for use with lights (so 5A round pin, or some roof-like location) or for dedicated low-power stuff like TV antenna amplifiers where no other power circuit was available, but consider it bad practice to have sockets that to any of the public look like they can be used for generic 13A loads but actually can't and also take out the lights in the process.

Edit: Also 512.1.2 on design current.
 
Last edited:
As I already said, I have no issue with sockets on light circuits for use with lights (so 5A round pin, or some roof-like location) for dedicated low-power stuff like TV antenna amplifiers, but consider it bad practice to have sockets that to any of the public look like they can be used for generic 13A loads but actually can't and also take out the lights in the process.
I get this, though if the lights come with a standard plug then you have the same situation if you installed FCU's where the plug requires removing/changing. I think maybe the electrician when installing should consider the position and so the likelihood of the sockets being used for other than their intended purpose.

Personally where possible I would try and mount them where they are not that practically accessible for general everyday use. This in my mind would satisfy good practice.
 
Personally where possible I would try and mount them where they are not that practically accessible for general everyday use. This in my mind would satisfy good practice.
100% this!

Edit: Labels are good as well, and given how modern labelling machines produce good professional-looking results it is not too much to put "Lights Only" or similar on any such socket.
 
Last edited:
The fact is that BS7671 lists a number of items that shall be connected to a lighting circuit. Can't remember exactly the reg, somewhere around 559.6 maybe....
The items include socket-outlets to BS1363-2, FCUs and other things.

So it is specifically permitted. Absolutely it carries NO comment, not even a C3 as it COMPLIES with the regulations.

Yes, it is possible that someone might plug a MIG welder in to the socket. If it makes you feel better, pop a label on it to say "maximum load 6amps".....But there is no danger whatsoever.
 
I tested a dive of a B&B probably 25 odd years ago in sunny Wellingborough. The loft had been turned into a room and all sockets had stickers on them stating 5A max. I discovered these had all been tagged from the lighting circuit all two core with no cpc.
 
TUT TUT , well its not just about BS7671 is it, come on people remember your days at the local tech college, its about adhering to the electrical craft principles we were all taught.
My tutors would be have a fit if they heard some of the comments going on here.
Practically IMO its not good for a circuit to be running over its CCC even if it only for a few seconds with big loads being plugged in untill its goes pop.
Then you could argue that being plunged in total darkness could warrant a C2 for safety reasons in some certain circumstances.
It would be a C3 for me all day long. We dont mix power with lighting circuits.
 
TUT TUT , well its not just about BS7671 is it, come on people remember your days at the local tech college, its about adhering to the electrical craft principles we were all taught.
My tutors would be have a fit if they heard some of the comments going on here.
Practically IMO its not good for a circuit to be running over its CCC even if it only for a few seconds with big loads being plugged in untill its goes pop.
Then you could argue that being plunged in total darkness could warrant a C2 for safety reasons in some certain circumstances.
It would be a C3 for me all day long. We dont mix power with lighting circuits.

Yes we do, we commonly have smoke alarms on lighting circuits.
 
looking at the pic in the OP, the socket in question is in the back of a kitchen wall unit.
Not very handy to plug in a heater, iron or kettle..

“Generally” we wouldn’t put a 13A socket on a lighting circuit, but if needed… for examples already given on the thread… I don’t see the problem when there can’t be a possibility of something too high a load being plugged in.
 

Reply to Sockets on a lighting circuit - C3 or C2? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
Hello What was the conclusion of your problem?
Replies
1
Views
826

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top