Hi there folks.
thought I had this one sorted but doesn't seem so. Called to domestic dual rcd db. Mcb tripping straight away on 'kitchen sockets' rcd does not trip! Ir test less than 1mohm. I thought I had it when I found a fault on one of the ring main legs. So with the customers consent downgraded breaker to 20 amp disconnected faulty leg and power now back on to sockets....but now as a radial. Called by customer to say sockets off again....rcd ok but mcb will not turn on.....'flash from breaker when you try to switch on'
Any ideas? Before I left radial IR readings all ok, appliances all plugged in, switched on and running fine.
thought I had this one sorted but doesn't seem so. Called to domestic dual rcd db. Mcb tripping straight away on 'kitchen sockets' rcd does not trip! Ir test less than 1mohm. I thought I had it when I found a fault on one of the ring main legs. So with the customers consent downgraded breaker to 20 amp disconnected faulty leg and power now back on to sockets....but now as a radial. Called by customer to say sockets off again....rcd ok but mcb will not turn on.....'flash from breaker when you try to switch on'
Any ideas? Before I left radial IR readings all ok, appliances all plugged in, switched on and running fine.