Design wise your loading would be 9x600=4500W so 19.57A at 230V. Then you need to remember it's 1.8 times the running current on start up so you need to size your breaker properly to allow for this. Im assuming it's similar in some respects to designing a circuit for a motor, if the motor runs at 5A you wouldn't allow for a cable that is capable of handling 6x that just for start up so the same would apply for the lighting. Think youll need atleast a couple of circuits for that lot and maybe a contactor to bring it all on with a type C breaker.