Hi guys,
I have asked this in another Electricians thread here. Firstly what size MCB usually required for lets say a 4kw solar panel load? Also it has been mentioned about RCD's protecting the solar panel circuit may not be a good idea. Any thoughts please? It's a brand new house build.i was planning to install RCBO's to each and every circuit. Thanks http://www.electriciansforums.co.uk...orum/98430-solar-panels-circuit-mcb-size.html
 
See below for info from Samil's product manual. Other inverter manufacturers may have different ideas.


[ElectriciansForums.net] Solar panel circuit MCB size?
 
A 16 A mcb is a reasonable starting point for a system that has a nominal 16 A output.
But it could mean running the mcb near maximum for many hours in the summer.
When in doubt read the manual!
ABB recommend 20 A for the 3.6TL and 25 A for the 4.2TL
SMA recommend up to 32 A for their range from 3000TL to 5000TL
 
There can be a problem with mcbs running hot near maximum rated current. Manufacturers' websites go into more detail. As the cable size for 4 kW PV is generally recommended to be 4 mm2 or larger, there is normally scope for a larger mcb.
 
Last edited:
I will be installing 6mm as I have that on site. No point getting 4mm. Any thoughts about 30mA protection? Am I asking for trouble?

I could always install a 20A MCB if 16A near the limit.
 
See below for info from Samil's product manual. Other inverter manufacturers may have different ideas.


View attachment 27461
Thanks, according to graph, i could in fact use 2.5mm cable as the inverter is next to the consumer unit. Having said that, installers mentioned 4mm. I've got 6mm, so will use that. I doubt if the circuit will more than 1m.
 
"Thanks, according to graph, i could in fact use 2.5mm cable as the inverter is next to the consumer unit. Having said that, installers mentioned 4mm. I've got 6mm, so will use that. I doubt if the circuit will more than 1m."

No, the graph is for the 3300TL model and is given as an example only!! 6mm cable is definitely fine though in a 4kWp domestic situation.
 
What about the dc side of the installation? How's this being run?
The DC side of the installation will be run in galvanised 20mm steel conduit which has been flushed into the corner (150mm). Inverter will be housed on ground floor. 2 x isolators have been installed in the loft by the installers.
 

Reply to Solar panel circuit MCB size? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

Hi My first post here, so apologies for any mistakes. I think it will be DIY job with electrician sign off if required, but would like to do as...
Replies
0
Views
188

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top