Wow, this thread took off a bit.
Personally I would be happy with dc cables running through my house properly protected/signed and prefer to have the inverter sited in a cool, convenient position rather than say in the loft.
If a customer still managed to drill into them, then put it down to Darwin's theories being played out.
Returning to the original topic as per the title, then for example the Schneider guidance is that when multiple mcbs are in a small enclosure then a 20% reduction in rating should be applied to determine the maximum service current. So for sustained operation at 16A, you should use a 20A mcb. In a hot environment the reduction increases.
http://www.schneider-electric.co.uk.../en/local/rti-catalogue-sections/SE7860_8.pdf
page 8/3
Personally I would be happy with dc cables running through my house properly protected/signed and prefer to have the inverter sited in a cool, convenient position rather than say in the loft.
If a customer still managed to drill into them, then put it down to Darwin's theories being played out.
Returning to the original topic as per the title, then for example the Schneider guidance is that when multiple mcbs are in a small enclosure then a 20% reduction in rating should be applied to determine the maximum service current. So for sustained operation at 16A, you should use a 20A mcb. In a hot environment the reduction increases.