Solar SWA cable run 10mm or 16mm | on ElectriciansForums

Discuss Solar SWA cable run 10mm or 16mm in the UK Electrical Forum area at ElectriciansForums.net

Joined
Mar 12, 2023
Messages
1
Reaction score
0
Location
Wales
Morning, I was just looking for some advice on what other sparks would do for the following scenario:-

A detached Garage is going to house a 7.4kw Solar Array and around 12kw of battery storage. The supply needs to return back to the main house (cable run approx. 22m) to DNO/consumer location. Would you opt for 10mm SWA or 16mm SWA ?
 
At full whack you will have circa 1.4% for 10mm and 0.9% for 16mm VD, that will be at nominal voltage, inverter will supply slightly higher voltage. You should just be OK with 10mm unless there are extremely long and power hungry lighting circuits
 
Probably not worth it for 22m, and there may not be room in the house, but you can always do as I did and run MV dc direct from the panels on 6mm or 10mm 2-core SWA, then put the inverter next to the CU.
I've never understood PV companies' obsession with always putting the inverter/s next to the panels, then running 230Vac back to the house, often in huge and expensive cable.
 
Not sure where I remember if from but I recall there being something about SWA actually being prohibited in PV installs? Whether that was between modules/strings or the array and the consumer unit I'm not sure, might be talking out my arse though so happy to be corrected
 
Not sure where I remember if from but I recall there being something about SWA actually being prohibited in PV installs? Whether that was between modules/strings or the array and the consumer unit I'm not sure, might be talking out my arse though so happy to be corrected
Answering questions at 4.01am?? That’s dedication
 

Reply to Solar SWA cable run 10mm or 16mm in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Sounds more positive.
Replies
8
Views
627
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top