I recently installed a Solarimmersion unit to work with our 4kw PV system.

The hot water tank is 1050mm high and I have just fitted a 27" immersion heater (as the old one was only 11")

I have also added an immersion jacket to the existing foam covering over the tank.

I've moved the cylinder stat up to just above the bottom of the 27" immersion heater, and the hot water is set to come on for 30 mins early morning and 30 mins late afternoon.

Cylinder stat set to 50 degrees, immersion set to abt 65 degrees.

The idea is obvious - I won't need to use the gas boiler while the weather is nice. But this still only means 2/3 of the tank will ever get heated unless the cylinder stat kicks in.

The solar immersion is designed to be used with a de strat pump, which I would really like to make use of, but I haven't got an idea of what I need and how to do it, even after searching google for 2hrs im none the wiser..

I have been reading a washing machine pump would do the job, is this correct?

Any help would be greatly appreciated

John
 
Are you sure you need to run a destrat pump? You may already have sufficient in the tank for your daily needs. Firstly, do you know what your daily hot water usage is at normal outlet temperature? This is unlikely to ever be above 45degC. Most calculations work on about 40ltrs per person per day. SAP works on considerably less, 25N+36 where floor area is unknown (SAP works on an outlet temperature of 47degC).

At 450mm diameter, the tank will hold about 140ltrs. This means 140ltrs stored at 60degC would give you the equivalent of 200litres, or 2/3 of the tank will give you 132ltrs. The other thing to bare in mind is that when the water in a cylinder stratifies, it does not stop at the level of the heating element, it will also pass below it. This is why when sizing a tank for solar thermal up to 30% of the solar volume (Vs) can be counted as daily volume (Vd). It is possible you could still have an effective volume of 150litres if the water is stored at 60degC.

Incidentallly, is this a vented or unvented cylinder? If it is the latter, please be careful what you do with the thermostats, or get a qualified person with an unvented ticket to look at this for you.
 
One other point. When storing water at 60degC, (or at any temperature at which there is a scald risk to infants and others), it is important to fit a thermostatic mixing valve either at the point of exit from the tank or at each point of use.
 
Are you sure you need to run a destrat pump? You may already have sufficient in the tank for your daily needs. Firstly, do you know what your daily hot water usage is at normal outlet temperature? This is unlikely to ever be above 45degC. Most calculations work on about 40ltrs per person per day. SAP works on considerably less, 25N+36 where floor area is unknown (SAP works on an outlet temperature of 47degC).

At 450mm diameter, the tank will hold about 140ltrs. This means 140ltrs stored at 60degC would give you the equivalent of 200litres, or 2/3 of the tank will give you 132ltrs. The other thing to bare in mind is that when the water in a cylinder stratifies, it does not stop at the level of the heating element, it will also pass below it. This is why when sizing a tank for solar thermal up to 30% of the solar volume (Vs) can be counted as daily volume (Vd). It is possible you could still have an effective volume of 150litres if the water is stored at 60degC.

Incidentallly, is this a vented or unvented cylinder? If it is the latter, please be careful what you do with the thermostats, or get a qualified person with an unvented ticket to look at this for you.

Thanks for the info Solar King, I feel I could definitely benefit from a de-strat pump, 2 reasons, first being during this time of year once the immersion has heated 2/3s of the tank there is still plenty of excess PV available which at present will just flow back into the grid, whereas if I fit a de-strat pump the solarimmersion can be set to turn the pump on at a certain level which will then eventually give me a full tank of hot water at no extra cost, instead 2/3s of a tank.

The problem of only having 2/3s of the tank heated, is that with the kids having a bath, me and maybe the mrs both having showers, there isn't much hot water left, and if the wife decides to have a shower before work it will be before the solar has kicked in to reheat the water, and may possibly not be as hot as she wants it, whereas a full tank of hot water should be plenty.

Re which system we have, I believe it is a vented system as we have tanks in the loft.

So can anyone point me in the right direction of where to start with this de-strat pump installation?

John
 
a destrat pump should be pretty simple to sus out if you know what you're doing, but IMO it's really one of those things where if you have to ask the question then it raises serious doubts about your competence to carry the work out.

so for that reason, I'm ooot.
 
A de-strat pump would either need to be bronze (usual in pumped hot water systems) stainless steel or high tmeperature plastic, it simply acts as a 'short circuit' betweeen the top (hot water outlet) and bottom (cold water inlet) of the cylinder. - It needs to be able to be able to be used in a 'potable water' installation.
Grundfos Comfort | Grundfos
or
Grundfos make a model PU.120 for example which is plastic bodied for potable water applications. You wont find it on the Grundfos website, the info is on the Euro Boiler Parts website. PU 120 Grundfos Pump 1 Plastic Body Replacement Grundfos Bronze Pump (It's not officially available in the UK :) as Grundfos UK don't talk to Grundfos EU )

Important note: You need to be a competent plumber to install and a competent electrician to wire in.
 
I fitted a 36" immersion and whole house TMV to my 150L tank and despite running at higher tank temps my system was still shutting off at around mid-day. Note the higher temps will give scale problems in hard water areas.
I looked at fitting a de-strat pump but found that fitting a second immersion (11") via essex flange to the bottom of the tank was a much easier and cheaper route in my case. Fitting the flange, although straight forward, is not something I'd recommend a diy'r try unless very competent.
I'm switching my home made diverter manually between the two immersions at the moment until I get the software to do it for me, but I think your unit could be set to change to the bottom immersion after the top immersion has been off for x-minutes.

With a de-strat pump during the winter you risk stirring the tank after heating the top of the tank when the sun is going down and ending up with a tank of luke warm water. With two immersions you will nearly always have the top of the tank hot enough for at least one bath in the winter and on good days the bottom immersion will increase that.

Despite my bottom immersion limiting at 65C instead of the 75C on the spec sheet it is still making a big contribution.
The attached graphs show two bath draws on the top immersion setup and two bath draws plus a next morning shower draw on the two immersion setup.
The temp sensors are located 8" from top, middle and 6" from bottom of my tank.
[ElectriciansForums.net] Solarimmersion installed - Really need some help installing a de strat pump[ElectriciansForums.net] Solarimmersion installed - Really need some help installing a de strat pump
 
Last edited:
Hi Dijon, looks like someone has a bath at 7pm and someone a shower at 8pm :)
I've PM's you with a couple of questions, as I also monitor the cylinder using openenergymonitor.org products.
 
Hi Dijon, looks like someone has a bath at 7pm and someone a shower at 8pm :)
I've PM's you with a couple of questions, as I also monitor the cylinder using openenergymonitor.org products.
They are both quite large 7pm and 8pm bath draws but they look very different due to the different temp distributions at the start of the first bath. Only the top and btm immersion graph shows the much lower draw from a shower at about 7:45am.
 
Here is another graph screenshot taken a few minutes ago. It shows the tank heated on the top immersion until 12am and then switched to the bottom immersion. I am now going to switch it back to the top to use the remaining sun to top up the top of the tank. Note that it has been limiting since about 3pm even on the btm immersion

.[ElectriciansForums.net] Solarimmersion installed - Really need some help installing a de strat pump
 
Hi,

Thanks for the info, fitting a second immersion (11") via essex flange to the bottom of the tank is definitely something worth considering and would definitely solve the problem of only the top half of the tank being heated, the solarimmersion can be wired to control a second immersion too, when the 1st has reached its temperature.

I still have the 11" immersion I removed to change for a 27" version, so I can re use that too.

My question though, how can you fit a flange and immersion heater to the bottom of the tank if the coil inside the tank is at the bottom too, wouldn't this be in the way?

Any links to the actual Essex flange I would need?

John
 
Hi,


My question though, how can you fit a flange and immersion heater to the bottom of the tank if the coil inside the tank is at the bottom too, wouldn't this be in the way?

Any links to the actual Essex flange I would need?

John

Good point,
I fitted my immersion between the bottom coil and the next coil up but it was difficult to do without them being in contact which I though might cause galvanic corrosion between the coil and the immersion. Basicallly I drilled the pilot hole through the tank then stuck an electricians screwdriver through the hole to determine the position of the gas heated coil then lifted the pilot hole an inch to get the best position between the coils. This might not be the best way to do this but it worked for me. YMMV and all that. It might be more sensible to drill just above the externally heated coil but then the immersion won't be right at the bottom of the tank.
I used the mechanical flange and 11" immersion from toolstation because they where about as cheap as I could find and also because I had one within driving distance of me.

http://www.toolstation.com/shop/Mechanical+Flange/p38614
 
Good point,
I fitted my immersion between the bottom coil and the next coil up but it was difficult to do without them being in contact which I though might cause galvanic corrosion between the coil and the immersion. Basicallly I drilled the pilot hole through the tank then stuck an electricians screwdriver through the hole to determine the position of the gas heated coil then lifted the pilot hole an inch to get the best position between the coils. This might not be the best way to do this but it worked for me. YMMV and all that. It might be more sensible to drill just above the externally heated coil but then the immersion won't be right at the bottom of the tank.
I used the mechanical flange and 11" immersion from toolstation because they where about as cheap as I could find and also because I had one within driving distance of me.

Toolstation > Heating > Central Heating > Mechanical Flange

I think this is definitely the best route for me, as I already have a spare 11" immersion heater, just need to get hold of the correct flange and have a look inside the cylinder to see if I can fit can fit the immersion at the bottom between internal coils.

Has anyone got any info on the internal coils of a 1050mm high cylinder? do they go all the way to the bottom? Whats the gap between coils?

John
 
Has anyone got any info on the internal coils of a 1050mm high cylinder? do they go all the way to the bottom? Whats the gap between coils? John
Every make of cylinder will be different! Even the same make made in different batches will vary...
 
Good point,
I fitted my immersion between the bottom coil and the next coil up but it was difficult to do without them being in contact which I though might cause galvanic corrosion between the coil and the immersion. Basicallly I drilled the pilot hole through the tank then stuck an electricians screwdriver through the hole to determine the position of the gas heated coil then lifted the pilot hole an inch to get the best position between the coils. This might not be the best way to do this but it worked for me. YMMV and all that. It might be more sensible to drill just above the externally heated coil but then the immersion won't be right at the bottom of the tank.
I used the mechanical flange and 11" immersion from toolstation because they where about as cheap as I could find and also because I had one within driving distance of me.

Toolstation > Heating > Central Heating > Mechanical Flange

Hi Digon,

Thanks again for the info, I think i'm going to give this a try.

That link to the immersion heater flange from toolstation, does it come with washers? is that item all I need (38614)?

Is there any difference between that and the immersion heater Essex flange (other than the price!)

http://www.amazon.co.uk/gp/product/B008C8T9CW/ref=pd_lpo_k2_dp_sr_1?pf_rd_p=103612307&pf_rd_s=lpo-top-stripe&pf_rd_t=201&pf_rd_i=B008C8T990&pf_rd_m=A3P5ROKL5A1OLE&pf_rd_r=1328J7R5GHS5BNC7EYEJ


Thanks again

John
 
As an Amazon Associate Electricians Forums may earn a small commission from qualifying purchases.

Reply to Solarimmersion installed - Really need some help installing a de strat pump in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

By the time you've dealt with isolator valves that won't shut off and drain valves that won't open, half a day will be gone before you've removed...
Replies
5
Views
787
The 4 pumps are :- 1. boiler to cylinder 2. C/H and UFH circulating pump 3. UFH dedicated pump after manifold 4. DHW circulating pump. (this just...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top