714gold714

Hello go easy on me

I have a job for a friend (yes im part p) mate wants X2 serperate outbuildings wired with X1 double socket in both and a small batten holder light inboth(spur out of socket with 13amp SFS) would this be ok? circuit would be ring main (32 mcb and rcd protected) would it be ok to do the job like this or shall i run a new circuit in in each outbuilding with own 2 way board? mate just wants it cheap as possible as tenants are renting the place

P.S sockets with be for X2 washing machines, its also a tns system

Any advice would be great
 
if both washing machines are on heat cycle at the same time,with anything else plugged in, it may be too much for your 13A FCU.

better to run separate distribution circuit/s from house CU.
 
thanks for the reply i got it wrong it X2 fridges that shall be going outside, iv just noticed aswell somebody has a run a cold feed into 1 of the outbuildings for maybe a washing machine? will that need bonding? all gas and water in house is bonded

thank you
 
also if i run x2 circuit outside would i need to fit a consumer unit in each? as im just worried about having rcd's back to back. as i could just put a 13a sfs next to socket and use that for light?
 
Tel, the SFS is for the light, one in each outhouse.

714 (OP), that should be a 3A fuse in the spurs. Sub board for each is way OTT. If water pipe comes from the house (albeit underground) and if the house is properly bonded for services then no need for additional bonding imo, but others may see it differently.
 
install a 4mm radial for both buildings and spur off for your lights peice of pi.. just choose the correct materials and use correct methods ie armoured to a box and then t&e etc


if the house is equipotental bonded already at the incoming mains gas and water theres no need to bond additional supplementary water pipes
 
Last edited by a moderator:

Reply to some advice needed please :) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
1K
  • Question
Take your photo on phone. Screenshot it to replicate it, then crop out the excess screen. Brings the image file down to a reasonable size. Was...
Replies
4
Views
959
Size of consumer unit is entirely up to you - a two module will suffice but for the couple of quid more then personally I'd go a size up so that...
Replies
3
Views
4K
K
  • Question
I agree... I've spent quite some time throwing numbers into a spreadsheet about this one. My conclusion was (with current costs) that for most...
Replies
11
Views
5K
At 3kW, 16A is enough.... I’m assuming you’re in UK? Where is SWE? Trouble is, the questions you are asking could be answered by your...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks