Guys,
A few things I experienced this week.
First one was where I had installed a solar installation. Basically completed the install fired up the inverter and was promptly givena red light indicating an "isolation fault." This was on a Samil River Solar inverter which ur company is just trialling. Anyway, after testing I found my ZS was 0.4 ohms, the system was PME.
I thought this was a bit high so I investigated and eventually found no earth connection on the circuit I had instaled, the termination wasn't made. What I cannot understand though is how I was able to obtain a ZS reading at all.
The instrument is a new an in calibration megger 1720 with no malfunctions and the batteries are only two weeks old.
On a proteus isolator you have a back to front terminal and you cannot see the termination, its effectively blind. Anyway the earth was not made and it just pulled straight out when I tugged at it.
QUESTION: How the hell did I get a ZS reading?!!
Its baffled me.
Anyway next question/problem.
On a TT system on Friday I measured a ZE on a TT system of 2.79 ohms. R1+R2 was 0.28 giving a ZS of 3.07 ohms, I didn't actually measure the ZS but just added R1+R2
Looking at my regs book now I can see the max ZS for a 16A type b rcbo is 2.87 ohms so I am outside of this.
Without performing a calc to see wether 4mm cable could have brought down the resistance of my R1+R2 and ZS within limits, I have a more demanding question,
If TT ZE is allowed up to 21 ohms, how do you meet maximum ZS stated in regs for a TT system?
I appreciate any feedback,
Dan
A few things I experienced this week.
First one was where I had installed a solar installation. Basically completed the install fired up the inverter and was promptly givena red light indicating an "isolation fault." This was on a Samil River Solar inverter which ur company is just trialling. Anyway, after testing I found my ZS was 0.4 ohms, the system was PME.
I thought this was a bit high so I investigated and eventually found no earth connection on the circuit I had instaled, the termination wasn't made. What I cannot understand though is how I was able to obtain a ZS reading at all.
The instrument is a new an in calibration megger 1720 with no malfunctions and the batteries are only two weeks old.
On a proteus isolator you have a back to front terminal and you cannot see the termination, its effectively blind. Anyway the earth was not made and it just pulled straight out when I tugged at it.
QUESTION: How the hell did I get a ZS reading?!!
Its baffled me.
Anyway next question/problem.
On a TT system on Friday I measured a ZE on a TT system of 2.79 ohms. R1+R2 was 0.28 giving a ZS of 3.07 ohms, I didn't actually measure the ZS but just added R1+R2
Looking at my regs book now I can see the max ZS for a 16A type b rcbo is 2.87 ohms so I am outside of this.
Without performing a calc to see wether 4mm cable could have brought down the resistance of my R1+R2 and ZS within limits, I have a more demanding question,
If TT ZE is allowed up to 21 ohms, how do you meet maximum ZS stated in regs for a TT system?
I appreciate any feedback,
Dan