Hi
I've bought a new face plate for the plug socket in the bedroom. I went to install it so i turned the electrics off and all the lights go off fine but the plug sockets in the bedrooms upstairs and the living room at the front of the house remain active. Does anyone have any ideas as to why this is? Our electrics are rather old but surely they should still turn off?
Thanks in advance.
 
IMG_2264.jpg

Thanks for replying. I turned off the two switches circled in the attached image.
 
IMG_2264.jpg

Thanks for replying. I turned off the two switches circled in the attached image.
Right thanks, what exactly made you think that the sockets were still active your words not mine?
Did you carry out the safe isolation procedure?
 
My guess is that there is a 2nd fuseboard ...... with more fuses or breakers....

You are wise to question what you appear to have noticed!
 
No i didn't carry out this test but everything that was plugged into the bedroom socket was still lit up and turned on ?

Hi IPF i have just looked and the tails go up into a black box that isn't very easy to get to or see but it appears to be another switch that i didn't know was there. I imagine this must be the switch to the remaining active sockets? which i imagine is the answer to my problem, i'll try this in the morning to see if i get any luck.
 
Hi bud,i would be very careful with an old,possibly frangible switch,such as that,bearing in mind the lack of ready isolation possible.
 
That is a rather old consumer unit and you are correct to get an electrician on board.
 
Earth system needs looking at, definitely. No evidence of TN, unless there's an TNS main term somewhere out of sight, which I would doubt.
I know there's an earth wire at the remote db, probably that going behind the mounting board but where is it from, the Wylex? If so, that supply is pretty new and I've a feeling it may be TT and if that's the case....well....an old voltage operated ELCB for one board and sfa for the remote one.
If I'm correct, what sort of qualification or experience did that supply installer have?
Tom......get your qualified mate to bring his test gear and have a good look.
 
Right thanks, what exactly made you think that the sockets were still active your words not mine?
Did you carry out the safe isolation procedure?
safe isolation?
1. stand in bucket of water, metal bucket is best.
2. complete circuit with body
3. locate isolation of circuit if still live
4. repeat step 2 and 3 till circuit proved dead
 
Once the qualified mate has had look at this, I fear his recommendations may result ultimately in a nice big bill!
That hidden rewire able switch fuse is truly ancient, as is most likely, the wiring attached to it.
Turning to the Wylex board, that's obviously been well messed, around in its time. The letters written above the fuses refer to red (30A), blue (15A) and white (5A) fuses, which is not the order the fuses are in now, and the small piece of metal missing from the cover, directly under the 5A MCB is 'interesting'. Possibly the result of someone levering out a live fuse with a metal screwdriver. I bet they didn't do it again.
Both MCBs have probably been fitted to make restoring power quicker and easier following frequent tripping of the two circuits, either because of overload or short circuit.
"Can of worms" comes to mind, and the tin opener is at the ready.
 
havent read any replies other than the OP, are you sure its not old storage heaters that have been turned into sockets? if so those sockets will only work at off peak times
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Wales

Thread Information

Title
Some of my plug sockets remain active when turning off electrics.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
Tom Cossey,
Last reply from
elsparko,
Replies
29
Views
3,302

Advert

Back
Top