Looking at possible job for customer.
Basically I intend to split tails to supply an rcd supplying, submian feeding additional CU. Therefore bypassing the old wylex reirable unit which customer dosent want the expense of changing.
Customer wants to know why I can't put just put the RCD before the old wylex cu to protect whole existing installation and then feed submain from a rewirable in here?
Have told him that because rating of a 3036 is 1ka this wont be sufficient as PFC is higher than this. Is there any other additional reason which I have missed ? Basically this chap is an electrical engineer, member of IEE etc, sound chap but has been reading part P doc, regs etc and would be nice to back to him with as much detailed info as possible... maybe quoting a reg or 2?
Many thanks,
Sy
Basically I intend to split tails to supply an rcd supplying, submian feeding additional CU. Therefore bypassing the old wylex reirable unit which customer dosent want the expense of changing.
Customer wants to know why I can't put just put the RCD before the old wylex cu to protect whole existing installation and then feed submain from a rewirable in here?
Have told him that because rating of a 3036 is 1ka this wont be sufficient as PFC is higher than this. Is there any other additional reason which I have missed ? Basically this chap is an electrical engineer, member of IEE etc, sound chap but has been reading part P doc, regs etc and would be nice to back to him with as much detailed info as possible... maybe quoting a reg or 2?