Hi all,

Thought i would throw this one out there,

Client has overhead supply coming into house and also has some outbuildings and requested a new supply from the DNO so he can have seperate bills for business use, i came along to fit a new dist board to the new supply, on this i fitted a split load board with 2 50 amp sub mains (existing) going out to the out buildings both with rcds upfront, when the installation was energised both rcds trip, so immediately you think got to be the neutrals on the wrong rcd, checked and all fine, turn on one supply and all fine turn on the other to the stable block and takes out both rcds even though they are going to different areas on the land and risk of a borrowed neutral somewhere is very slim,


anyone got any ideas why both rcds would trip
 
Are they new RCD's or like the sub main old existing ones?

If New could they be fauly? if old could they be faulty? Ramp test will tell.

It would seem that you may have a fault somewhere on that stable block, have you done any testing at all like IR. ?

When you say the DNO have supplied another supply, do you now have a 3 phase supply covering all installations or 2 x single phase supplies?

This to me seems you have a common neutral somewhere,and you have a fault that is being picked up on the neutral, possible N-E fault and therefore activating both RCD. which you would have on a 3 phase supply, and could also have even on 2 individual 230volt supplies as the DNO themselves may coupled them up.

It may even be something as stupid as wrong polarity somewhere.
 
Last edited:
All new rcds, ramp tested all fine, all the normal tests come back fine and they have single phase and the DNO has just taken another leg off the incoming overhead, to get the outside supplies back on we moved them both onto the same rcd and it holds fine
 
Was there any load on the buildings when you switch on ?

On your original OP you stated the stable block when turned on takes out both RCDs, now you say if you connect up the both areas on to a singular RCD , I assume it's the stable and AN other, it holds?

Have you tried switching on one at a time? Have you tried the stable on each RCd alone and see what happens?

Is there anything in the stable that is likely to have had protective conductor currents when it was tripping both RCD, but could have then been off when you doubled onto a single one?
 
Was there any load on the buildings when you switch on ?

On your original OP you stated the stable block when turned on takes out both RCDs, now you say if you connect up the both areas on to a singular RCD , I assume it's the stable and AN other, it holds?

Have you tried switching on one at a time? Have you tried the stable on each RCd alone and see what happens?

Is there anything in the stable that is likely to have had protective conductor currents when it was tripping both RCD, but could have then been off when you doubled onto a single one?

They were only under minimal load, if you switch on rcd 1 first, holds fine, turn on rcd 2 both rcds trip, if you turn on rcd 2 first it holds fine and then turn on rcd 1 they both trip
 
I’m getting a horrible feeling I’ve seen this before, that’s why I asked for a picture.
that was my first thought and all the linking cables are definately going to the correct terminals, but i havent got any pics but there are other circuits on both sides which when they are on they hold fine
 
I'm reaching a bit here: Guess it's a TT site.... if you had a leakage fault on the main house, or on one of the two outbuildings, could it be the effect of two or more rods back-feeding that leakage current onto the new circuits????

Might be worth spending a few minutes with the leakage clamp out.
 
I'm reaching a bit here: Guess it's a TT site.... if you had a leakage fault on the main house, or on one of the two outbuildings, could it be the effect of two or more rods back-feeding that leakage current onto the new circuits????

Might be worth spending a few minutes with the leakage clamp out.
i did think about that as well, but now i have moved both the sub-mains back on to the same RCD if there was leakage i thought it would of raised the current and tripped again but it is holding fine
 

Reply to Something strange in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
654

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top