C
Cider
Hi all
New to this but am i correct in thinking (having looked at gn3, on site guide and another testing book) that the measurement taken for earth rod resistance is also the ze as both tests seem to be taken in the same way (megger connected between disconected rod and phase live side of main isolator turned off).
Also the earth fault reading taken in ohms is multiplied by the voltage to give earth fault current divided by 1000 to give kpa.
Short circuit test between R1 and N give direct kpa.
Both taken with rod connected but main switch off.
Hope this makes sence.
Be kind if im wrong!
Cider
New to this but am i correct in thinking (having looked at gn3, on site guide and another testing book) that the measurement taken for earth rod resistance is also the ze as both tests seem to be taken in the same way (megger connected between disconected rod and phase live side of main isolator turned off).
Also the earth fault reading taken in ohms is multiplied by the voltage to give earth fault current divided by 1000 to give kpa.
Short circuit test between R1 and N give direct kpa.
Both taken with rod connected but main switch off.
Hope this makes sence.
Be kind if im wrong!
Cider