Sorry but Ra = Ze ? | on ElectriciansForums

Discuss Sorry but Ra = Ze ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

C

Cider

Hi all

New to this but am i correct in thinking (having looked at gn3, on site guide and another testing book) that the measurement taken for earth rod resistance is also the ze as both tests seem to be taken in the same way (megger connected between disconected rod and phase live side of main isolator turned off).

Also the earth fault reading taken in ohms is multiplied by the voltage to give earth fault current divided by 1000 to give kpa.
Short circuit test between R1 and N give direct kpa.
Both taken with rod connected but main switch off.

Hope this makes sence.

Be kind if im wrong!

Cider
 
What is this earth fault reading that is taken in Ω?
Do you mean the earth fault path resistance taken in Ω?
Do you then mean that the measured voltage is divided by the earth fault path resistance and then divided by 1000 to obtain the Prospective Earth Fault Current in kpa, or perhaps the more commonly used units of kA?
 
Last edited by a moderator:
sorry, KA not kpa.
I got 96.1 ohms before i repaced the rod which had an Ra of well over 200.
Ive not had a chance to do fault currents again but want to get an understanding of the earh fault reading.

Thanks again.
 
Ze/Ra is the term given to the resistanc of the earth fault path.
Your reading of 96.1Ω is OK, but not fantastic. Obviously it's better than over 200Ω.
Your PEFC will be quite low, using a nominol voltage of 230V, it will be 2.39A, if you wanted to divide by 1000 it will give a kA of 0.00239kA.
This is to be expected with TT installations, and is why an upfront RCD is required to provide ADS.
Your PSSC will be a lot higher, more in common with TN-S and TN-C-S installations.
 
sorry, KA not kpa.
I got 96.1 ohms before i repaced the rod which had an Ra of well over 200.
Ive not had a chance to do fault currents again but want to get an understanding of the earh fault reading.

Thanks again.

Cider.
it's important to get the units correct from the earliest stage of your learning. To that end:
it's kA (for kilo amps), not KA [note the small k in the correct term].

FYI: kPa is kilo pascals and are units of pressure

Have a look here to brush up on your units:
International System of Units - Wikipedia, the free encyclopedia
SI derived unit - Wikipedia, the free encyclopedia
 

Reply to Sorry but Ra = Ze ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top