Hi
I have a customer who has a cooker plugged into a 45amp cooker socket (cooker cable is 2.5 flex) with a 10mm cable back to a 32amp breaker! They have recently had the cooker serviced and have been told this cooker should be wired directly as during it's self clean cycle it used 3.6kw for 1.5 hours.
Can the cooker flex be directly wired into the cooker switch and will it be capable of taking the 32amp breaker out? The flex on the cooker is 1.5m
Thanks in advance