same thing IMO. never heard it described as Sp&N. though. just a D/P isolator, 1 pole for L and 1 pole for N.
 
one's fused and one isn't, according to what you have posted. sounds like the SP&N is the fused one. only the L can be fused.
 
A switch disconnector has to:-

Provide an effective clearance between the supply and the load appropriate to the voltage applied.
Provide a means of locking in the 'Off' position. (Padlocking)
Provide a true indication of the contact state.
Provide a safe disconnection from the supply even under fault conditions

A double pole switch dosn't have to meet all these set requirements.....

The two terminologies function the same more or less although when talking switch disconnectors you may also have 'early make - late break' on the neutral especially on 3ph... the uses of the 2 terms relates to requirements of the isolation needed...
 
So for single phase supply, any one of these can be used to isolate the main supply if needed to work. Difference is one with fuse and other without.
 
A switch disconnector has to:-

Provide an effective clearance between the supply and the load appropriate to the voltage applied.
Provide a means of locking in the 'Off' position. (Padlocking)
Provide a true indication of the contact state.
Provide a safe disconnection from the supply even under fault conditions

A double pole switch dosn't have to meet all these set requirements.....

The two terminologies function the same more or less although when talking switch disconnectors you may also have 'early make - late break' on the neutral especially on 3ph... the uses of the 2 terms relates to requirements of the isolation needed...

Commonly called off load and load breaking, switch disconnectors!!
 

Reply to SP&N isolator and double pole isolator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
159
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
526
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
474

Similar threads

For a TN system neutral is deemed at earth potential.
Replies
6
Views
335
M
  • Article
Isolation valve with double check valve Does anyone fit these internally for outside tap installation? Instead of an isolation valve and a...
Replies
0
Views
91
Matt0029
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top