Yes mate,there are bends in it !
widdler,just ran by your calcs again and it looks like we are well over the limit, are your calcs regulation or reccomendation ? thanks for your time.
well,believe it or not the answ is yes, you can physically do it, cos i have done it,bends and all,plenty of the yllow stuff and pull like ****. i wasnt happy doing it but the ****e firm am working for insist on it. Theyre saving on conduit runs !!!
Did install of Cat5E for a company, the runs were from a roof space with containment provided by electrical contractor;
9 in 20mm conduit
12 in 25 mm conduit
All runs had at least 3 90 degree bends.
Ended up soaking in Yellow77 and wrapping around a scaffold pole to get leverage.
Cables must've stretched but passed certification tests just fine!