Hi all. I will do some ring, lighting, smoke alarms on the new loft for my client. I haven't space in the old fuseboard, so I thought to install a second small fuseboard. Should I connect earthing cable to the pipe? Thanks for any help.
 
If the pipe is already suitably bonded to the existing board, then you don't need to bond it again from the new board.

If you're splitting tails in a henley block or similar then adding an earth bar with suitable earthing cable to the new board might be a handy place to put the main bonding in for future ease of testing/identification.

But if the existing board is the MET then also fine to just run suitable earth to the new board from there if there is space.

If the existing bonding is 6mm then now would be a good chance to upgrade it to 10mm
 
@Dartlec beat me to it.

I would say "No, you don't need to bond it".
My reasoning is:
The water pipe should be bonded at the point of entry to the building anyway (assuming it isn't plastic where it enters). So main protective bonding requirement should be already fulfilled. If you want to be sure you could continuity test the pipe with a wander lead to the MET.
Unless the new board is in a bathroom or other 'special location' there isn't a requirement for supplementary bonding either.
So I can't see a good reason to bond it again.

(It was once the case to say "If in doubt, bond it". Some still say this. But I don't think this is a good answer as by following this mantra things can become live in fault conditions that otherwise wouldn't.)
 
But if the existing board is the MET then also fine to just run suitable earth to the new board from there if there is space.

I was taught never to earth a board from another board and to split the earths in a Lucy block or other suitable accessory.

Never questioned it but now I am. Is it fine to take an earth from an existing board?
 
I was taught never to earth a board from another board and to split the earths in a Lucy block or other suitable accessory.

Never questioned it but now I am. Is it fine to take an earth from an existing board?
I don't see any reason why not so long as there are enough free terminals able to take the (probably) 16mm conductors. After all if you took a sub-main then it comes from there.

However, I also think it is good practice to have the MET separate from the CU so it is clear for inspection and test where the DNO earth and extraneous bonding goes, and in that case you would simply take each board's earth from the MET block.

Which is what you already do and, I believe, the best way.
 
(It was once the case to say "If in doubt, bond it". Some still say this. But I don't think this is a good answer as by following this mantra things can become live in fault conditions that otherwise wouldn't.)
I would still suggest that for anything that:
  • Could introduce a potential by means of it carrying cables, or being somehow in contact with the Earth (below 20k ohm) so "extraneous"
  • Can be touched when also in contact with anything else on the CPC circuit
For example, I would not bond radiators as the pipe work should already be bonded and then they can't introduce anything else, but I would bond cable tray carrying any sort of power cable.
 

Reply to spare fuseboard in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
889

Similar threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
716
hI Gent's. I I can explain this spur line briefly, maybe someone can help me? Everything is Spur, no rings. Inside of the house and main fuse...
Replies
0
Views
322

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top