just been to a job where rcd main switch for 3 phase db has developed a fault - tripping on load from 2 different circuits - so I need a replacement. HAGER 63 AMP (AT LEAST), 30mA 4 POLE RCD.

they're available online at silly money, which I may have to pay, but one of you may have one lying around and I'd be more than happy to give you £50 for it?

regards, me
 
Are you 100% sure it's the RCD at fault and not a fault on each of the 2 affected circuits??
 
well it's tripping on load with the oven, then also with u/f heating.

highly unlikely - but not impossible - that they've both developed an earth fault at the same time.

there's another rcd for a different section of the db - exactly same type, working fine - i'll swap 'em over tomorrow to verify faulty rcd.........or not!
 
i quickly checked connections, lots of which were loose enough to get several turns on the terminal screws, so will probably be recommending a bit of a once over anyway.
 
i quickly checked connections, lots of which were loose enough to get several turns on the terminal screws, so will probably be recommending a bit of a once over anyway.


Sounds like it may need it.

Expect to pay around £100 for a new one.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
sparkies - hager rcd required!
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
maffa ent,
Last reply from
Guest123,
Replies
5
Views
2,183

Advert

Back
Top