Evening all,
today i was doing a fuse board upgrade. On completion i was testing ze and water pipes were sparking. On further investigation found no earth presesnt.
tested ze on non trip mode and got 500 ohms. Fitted an earth rod and managed to get it down to 6.38 ohms with a pfc of 39 amps.
what do i do from here. ive notified customer of hazard and energy supply company will be coming down to have a look.
are there any measures i need to take for extra protection? do i need to fit an rcd on the supply end?