Hi Guys,
Quick sanity check please.
I'm wiring a conversion which has spray foam insulation on all the outside walls (around 50-75mm thick) between studs. I've not come accross this stuff before.
My ring main will be clipped direct under the suspended floor, but will run for approx 500mm in the foam. I've dug a channel in the foam for the 2.5mm t and e. This will then be plasterboarded over.
Now I've decided that as the cable will prbably not be touching the plasterboard, and its enclosed in thermal insulation I should derate the cable to 13.5A, so I'm going to use a 20A MCB. Does this sound reasonable?
So in summary I've decided its Method 103, but its not really as the insulation doesn't serround the cable, but its not 102 because the cable doesn't touch the plasterboard, thoughts?
thanks