A

abacusf

Hi Guys,

Quick sanity check please.

I'm wiring a conversion which has spray foam insulation on all the outside walls (around 50-75mm thick) between studs. I've not come accross this stuff before.

My ring main will be clipped direct under the suspended floor, but will run for approx 500mm in the foam. I've dug a channel in the foam for the 2.5mm t and e. This will then be plasterboarded over.

Now I've decided that as the cable will prbably not be touching the plasterboard, and its enclosed in thermal insulation I should derate the cable to 13.5A, so I'm going to use a 20A MCB. Does this sound reasonable?

So in summary I've decided its Method 103, but its not really as the insulation doesn't serround the cable, but its not 102 because the cable doesn't touch the plasterboard, thoughts?

thanks
 
Can you not put the 500mm run in conduit, then it would be ref method A? Better than method 103.
 
If this a general domestic socket ring circuit and not a kitchen ring, then the chances of that cable being subjected to anywhere near it's current rating is slim to remote. Personally i wouldn't bother applying any de-rating factor....
 
If this a general domestic socket ring circuit and not a kitchen ring, then the chances of that cable being subjected to anywhere near it's current rating is slim to remote. Personally i wouldn't bother applying any de-rating factor....

Couldn't agree more but you either go by the book or you don't ...and who's to say the boiler won't fail meaning they plug in a few convection heaters and do load the circuit to the hilt!.. but yes know where your coming from.
 
Couldn't agree more but you either go by the book or you don't ...and who's to say the boiler won't fail meaning they plug in a few convection heaters and do load the circuit to the hilt!.. but yes know where your coming from.

For the sake of 500mm, i doubt if it'll make the slightest bit of difference, in your above scenario to be honest...
 
For the sake of 500mm, i doubt if it'll make the slightest bit of difference, in your above scenario to be honest...


As the OP has cut a channel anyway must agree and the operating temp# of the cables insulations is 70c then we know common sense prevails here but was just saying and if we are to believe the issues with said domestic rings in thermal and assume they are not worse case scenario's then 500mm is 500mm and is a weak link.... ;)
 
Thanks for all the replys. I think I'll treat it as 102 and derate to 20A and use a 32 a mcb as normal. On the other circuits I'll pack the cable out to touch the plasterboard.

I don't really understand why touching a non heat conducting surface can affect the current carrying capacity though (as opposed to not touching, not as opposed to buried in insulation)
 
Thanks for all the replys. I think I'll treat it as 102 and derate to 20A and use a 32 a mcb as normal. On the other circuits I'll pack the cable out to touch the plasterboard.

I don't really understand why touching a non heat conducting surface can affect the current carrying capacity though (as opposed to not touching, not as opposed to buried in insulation)

If plasterboard was non heat conducting then there would be no need for insulation behind it :smilewinkgrin:
 

Reply to Spay Foam in Stud Wall in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
731
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top