Ian1981

-
Mentor
Arms
V.Nearly Esteemed
Joined
Sep 22, 2016
Messages
3,786
Reaction score
4,073
Location
North east
Well just as I thought I had this spd requirements down I attended the Niceic tech talk, with a speaker from the jpel/64 panel who is mainly responsible for the requirements of SPD’s and go figure a manufacturer of the product.
So I learned that installing a type 1 device at the origin and type 2 devices at downstream distribution boards is not enough ( where a LPS is required)
SPD’s are required wherever the zonal interface is penetrated from the outside (zone 0)
So coaxial cables, telecommunication cables, cables from one building to another etc all require protection where they enter the building and enter the building from zone 0.
As an example he showed us an estate where it consisted of over 40 individual SPD’s.
Bit of a ball ache really so I’m off to re-train as a plasterer as it’s less hassle
 
Well just as I thought I had this spd requirements down I attended the Niceic tech talk, with a speaker from the jpel/64 panel who is mainly responsible for the requirements of SPD’s and go figure a manufacturer of the product.
So I learned that installing a type 1 device at the origin and type 2 devices at downstream distribution boards is not enough ( where a LPS is required)
SPD’s are required wherever the zonal interface is penetrated from the outside (zone 0)
So coaxial cables, telecommunication cables, cables from one building to another etc all require protection where they enter the building and enter the building from zone 0.
As an example he showed us an estate where it consisted of over 40 individual SPD’s.
Bit of a ball ache really so I’m off to re-train as a plasterer as it’s less hassle

That would not help . Your trowel and float would need one.
 
I did an LPS course a few years ago and TBH we could have spent another week going through SPDs then...

It really adds to the price of a job when you have lots of zones within building, I do telecoms and it is a complete nightmare to do properly and to get the customer to pay for it.
 
My tiny mind is blown as I did not fully appreciate the actual requirements of the LPZ system and all the different cables entering the different zonal interfaces and the shear amount of SPD’s required
 
I did an LPS course a few years ago and TBH we could have spent another week going through SPDs then...

It really adds to the price of a job when you have lots of zones within building, I do telecoms and it is a complete nightmare to do properly and to get the customer to pay for it.

Out of interest do you get many strikes on the masts?
 
Out of interest do you get many strikes on the masts?
Not as often as you’d think. Most common cause of damage is from induced voltage from strikes further away, this is where the SPDs come into their own.

A direct strike on a building even with LPS can cause a significant amount of damage, luckily we don’t see many high magnitude strikes in the UK, ours are pretty feeble.
 
I am aware of the requirement for all services and incoming cables to be protected against surges from lightning in the lightning BS but all this is not within BS7671 so not a part of our remit surely?
 
Thing is the regulations cover cables upto 1000 v A.C and 15000 v D.C so cables in this bracket are fair game.

It was very much an eye opener
 
Last edited:
I carry out maintenance on a large CNC enginerring factory, Wire new machines, change damaged DOL etc and maintain service.

Although I try to work within the regulations (to the best of my knowlege) the original design was not carried out by me, its intresting to know where I would stand from a legal point of view if something were to happen like a fire or major damage to machines due to wrongly selected type of SPD or lack of SPDs. and of course om top of that we have AFDDs

Domestic settings are fairly simple but maintaining an older installation which is in constant services worries me, if you do the math SPDs should be installed in most suburban settings in the UK especially if your withing a few 100 mtrs of the substation. And AFDD are recommended in the BBB but if someone didnt recommended one and say something burnt down due to and arc or expensive machinery got damaged due to a surge then I am sure the insurance company's would get the contractor nailed to the cross even if that part of the installation was nothing to do with them.
 
Last edited:
You cant be accountable for what was designed and installed there beforehand but for any future work SPD's AFDD's need to be considered.
Put it in writing that you 'recommend' them or that should be fitted, cant be held accountable if powers that be decide to scrimp on the install cost and you'll have proof you need!
 

Reply to SPD’s requirements in electrical non domestic installations in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
832

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top