AngusSparkie

Hi all, my first post. Just been to see a job to change a fuse box to a 17th edition CU. Did some testing to see what I'll be dealing with. All seems well apart from 1 radial that has 3 ends of line. What are my options? Do I need to make a ring with a non fused spur? or can I use the highest Zs and put it into a 20A MCB? Each spider leg has 1x 1G skt, 4x 2G skts and 3x 2G skts. The radial/spider is currently fed from a 15A fuse. Not looked for JB's etc as didn't want to lift the floor coverings. Many thanks.
 
Thanks for the fast response. I was a bit worried as I couldn't find this in the regs. If I ever run a radial its always linear. This one splits from 1 into 3. Old houses I guess but if it complies, that'll do me. Thanks again.
 
Nothing wrong with branching radials, even the IET is endorsing them with their little pictures in the 17th. Not how I'd wire something from scratch, as it does mean multiple ends to test, but in the case your detailing as long as the circuit tests ok, just use the longest leg as your basis for selecting your OCPD and filling in the paperwork. If it is 2.5mm T&E just check for installation method as this may help you select either a 16 or 20amp MCB/RCBO.
 
Thanks all. Glenn if you read my post I ask if I'm ok to do what everyone else has suggested. I sought clarification as I could not find spider radials in the 17th ed. (I would be grateful for a page no.) and therefore sought clarification that they are ok even if the test results are all fine, which they are. I realise that this was popular in the 70's but that doesn't mean it's current and as I've said I can't find a reference to it in the regs hence my question. I would never wire like this and it wasn't covered on my 17th ed course. Regards.
 
Hi Angus, Tel's advice was spot on in post#2. You don't need to apologise for seeking clarification on something you're unsure about.

Others who have nothing constructive to say need to walk away without comment.
 

Reply to Spider Radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
988
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
494

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top