Did an EICR that passed 5 years ago
Several things in the picture raised concerns for me.
Comments please - photo at end
First photo shows a split concentric in use AFTER the meter, the supply is a TNC-S supply and the split concentric has the following items
Second photo
Gas meter (plastic incoming pipe) has copper outgoing pipe which goes underground and can induce
Several things in the picture raised concerns for me.
Comments please - photo at end
First photo shows a split concentric in use AFTER the meter, the supply is a TNC-S supply and the split concentric has the following items
- Single insulated neutral conductors that are accessible to touch C2
- Unsleeved cpc on the split concentric C2
- Single insulated line conductor- this is thicker than normal and may be aluminium (have put this down as FI)
- Split concentric cable has neutral and earth wrapped around the inner line conductor and appears therefore to have neutral conductors acting as a armour in case of a fault listed as FI
Second photo
Gas meter (plastic incoming pipe) has copper outgoing pipe which goes underground and can induce