Morning Peeps

If you find a fault on a ring and decide to split it, how do you guys decide where the middle of the ring is, or do you just split it anywhere that you think is central? Are there any tests that can be done to find the central point?

I just want to see what the general consensus is?

Cheers
Mark
 
you're splitting into 2 radials because of a fault

so do you not have to split where the faulty section is then?

or do you mean the ring isn't wired correctly?
 
Last edited by a moderator:
When splitting a ring due to trying to find a fault i dont generally worry about finding the middle of the ring, i am trying to find the faulty part. so i just split and test. and keep doing this until i find the fault. More times than not the ring will be split in many places by me to i find the fault, so finding the middle is not important.
 
Last edited:
I think you were right davelerave, Basically once u find the faulty cable, remove the damaged cable and stick both legs of the old ring on separate 20a breakers (as long as one of the legs wasn't the damaged part obviously)
 
Obviously it would be best to split centrally with an equal number of sockets on each new radial. Unfortunately it all depends on the faulty leg and where she is. As the lads have said, if there is no other way of rectifying then 20A radials is all we can do.
 
As lenny and the other guys, depending on the fault you could do the R1 R2 lest where you cross the legs , then take continuity readings at each socket when you find the higest reading you have found the center point of the ring , R1 R2, live of leg A to cpc of leg B and leg B live to cpc of leg A
 
Last edited by a moderator:

Reply to Splitting a ring in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
191
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Correction: Ignore that last bit, I got confused. The OCPD will still trip in time at the sum of the currents.
Replies
3
Views
683
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top