Hi all,

I have a cpc continuity fault on a ring main which only consists of 7 sockets and 2 FCU.

I have split the circuit and found that it is one of the legs coming from the C.U to the first socket.

Normally I would convert to 2 radials but this is not possible and also its concrete floor. The client does not want me to chase the wall and replace the leg.

Is it possible to convert to one radial on a 20a mcb?

The main appliances used would be kettle, microwave, boiler, fridge, freezer and tv.

Thanks
 
Can you not put the unaffected portion onto a 20a like you said, lose the damaged point and blank off. It could just be you have either a loose or open connection at board/ socket or even a fragmented c.p.c core within the sleeving inside the board (if it is T&E that is)
 
Oh right i see so if you split at damaged point power up one leg you get all sockets live with correct earth, other leg you get nothing live with no earth. 20a should be o.k as wirepuller says. Only doubt is it is a kitchen load with some reasonably heavy draw.
 
Yeah kitchen is possible the only problem.

The appliances plugged in are kettle, microwave, fridge and freezer. Plus spur for boiler and cooker hood.
 
convert to radial on a 20A MCB, as you suggest. if the customer has problems with the MCB tripping, then it's his own bloody fault for refusing to have the RFC reinstated.
 
Abit of a bummer when the customer doesn't want anything ripped up.

Like been said, convert the ring into a radial - so effectivley the first socket becomes the last and down grade to 20a. You'll then just have to advise the client about the possible overload issues if everything is on at once. Not much you can really do when the client doesn't want anything physically disturbed.
 
TBH you have L-L & N-N continuity so you have no issues with cables not being protected against overload by the MCB. The c.p.c is broken which is sending the Zs values above the permitted tolerance of the MCB, however as the circuit should be RCD protected to 30mA this eliminates the problem with disconnection times and fault clearance which would exist if no R.C.D was connected. Therefore i cannot see any immediate issues.
I stand corrected if somebody can highlight any condition i haven't taken into account. The R.C.D is the important factor here.
Although this warrants a C2 on an EICR if the client refuses correct remedial action to make this circuit comply as a ring the best thing you can do is detail the condition, reasons why it has not been rectified as to BS7671 and get it signed by the client. Cover your back, that is the best you can do.
 
Last edited by a moderator:

Reply to Splitting ring main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
710
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

https://www.amazon.co.uk/gp/product/B08CJ3VC79/ref=ppx_yo_dt_b_asin_title_o05_s00?ie=UTF8&psc=1 I use this, current clamps go round each outgoing...
Replies
3
Views
891
  • Question
As long as you can carry out all the necessary testing, certification, are insured to do the work and all is carried out to Amendment 2 of the regs
Replies
1
Views
724

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top