D

Dunx

There are two flats in a converted terraced house and at present there is one CU for both flats. I am rewiring the upstairs flat and then disconnecting/blanking of the original wiring. I plan to leave the downstairs wiring as is but remark up etc.

Upstairs I have calculated as 16mm T/E feed, its a one bed flat. 9kw shower, elec cooker, Immersion two rings plus OP storage heaters x 3. The new meter position will be in the hallway downstairs so I will have to run a new sub main via fused isolator to new CU upstairs. Not sure which is the best option for the OP fed tho. I could put in a timeclock/contactor arrangement and split the feed upstairs, or I could get a 5 wire meter fitted and run a second phase in 16mm singles. That way I won't have to install timer and contactor. What do think is the best option? Also where I blank off the original feeds to lights/sockets, there was only one lighting circuit and ring, do I need to put warning notices that there are live cables behind?! Ideally I would have preffered to rewire both as completely independant units but that is not an option!
 
Hi Dunx

Speaking as a meter installation engineer, you would be better off asking your supplier to fit a 5 terminal meter rather than messing about with a contactor and time switch. Just make sure you have your meter tails ready and identified for normal and O/P supplies or fit 2 x 100amp isolating switches berfore meter engineer arrives or he will just walk away and not fit the new meter.

Regards
Meterman
 

Reply to Splitting supply for two flats, sub main question! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
385
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
OP - is this T&E run on the surface or in conduit all the way? Or is any of it below the surface? I'm guessing not as you were talking about...
2
Replies
18
Views
2K
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
781

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top