how is a double socket spur on 2.5 protected from overload by a 32A mcb - I still think it's a good question!

The overload is governed by the two 13 amp plug tops, in such much 26amp is the maximum that can be drawn and odds of both the sockets being used to the maximum is very slim and if they were and others sockets were also being used the 32amp mcb would more than likely trip.

Diversity works in the real world, so you have to rely on it along with ones experience.
 
I would say overload has been omitted 433.3 due to the nature of the load, that being the fact that only one single or double may be connected.

Protection against fault current would still be provide via the 32 amp mcb.

Socket outlets now require rcd protection so zs wont be the overriding factor it will be the volt drop.

Chris
 
I would say overload has been omitted 433.3 due to the nature of the load, that being the fact that only one single or double may be connected.

Protection against fault current would still be provide via the 32 amp mcb.

Socket outlets now require rcd protection so zs wont be the overriding factor it will be the volt drop.

Chris

That's assuming a domestic-type situation.

A socket spurred off in an office under the control of etc. etc. in 20mm galvanised conduit or any of the other surface/earthed scenarios will still be limited by Zs and volt drop.
 
That's assuming a domestic-type situation.

A socket spurred off in an office under the control of etc. etc. in 20mm galvanised conduit or any of the other surface/earthed scenarios will still be limited by Zs and volt drop.

Well yes i was assuming a domestic situation, though non domestic will not necessarily be excluded from RCD protection, that would be down to designer type of load and any risk assessments etc

Chris
 
Last edited:

Reply to Spur From Ring in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

Outside socket… ok. But you say the fcu for boiler is beside the outside socket… is the boiler outside too? FCU’s have an IN and an OUT… the OUT...
Replies
2
Views
138
Many thanks. Very clear!
Replies
2
Views
188

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top