Is it an accepted practice to spur off a spur on a ring if the first spur has been run from 4mm cable. I've never done it as always been told to spur off a spur was a definate no-no, but is it ok with 4mm?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Spur off a spur in the Australia area at ElectriciansForums.net
You can then take a FUSED spur from an unfused spur, this is fine, and if you wanted take another FUSED spur from the previous FUSED spur.
what is protecting the additional cabling between unfused and fused spur.
1 spur per outlet or 1 fused spur with as many outlets as required after the fused unit
Have a look at appendix 15 in the BRB.
Yes, but it doesn't show a fused spur coming from a unfused spur does it?
Actually while a spur from a spur off a ring ,even wired in 4.0mm would not comply with the requirements for ring circuits, and hence should not be done,in practice it should not be a problem.Given that a radial wired in 4.0mm and fused at 32A can supply an unlimited number of sockets you would in effect be spurring a radial from a ring circuit fused at 32A,there would seem little difference.
Only problem then is if one leg of the ring fails, then you have a 2.5 with a 32amp breaker/fuse