Is it an accepted practice to spur off a spur on a ring if the first spur has been run from 4mm cable. I've never done it as always been told to spur off a spur was a definate no-no, but is it ok with 4mm?
 
I would assume that as long as you take your new spur feed from the supply side of the existing spur and ensure that it is correctly fused for the equipment it feeds, then it's perfectly OK.
 
You can take 1 unfused spur from each socket on a ring, eg, 10 sockets on ring can have 10 unfused spurs, 1 from each socket.

You can then take a FUSED spur from an unfused spur, this is fine, and if you wanted take another FUSED spur from the previous FUSED spur.

As long as each spur is fused then the regs allow it, as the cable between the spurs is protected.
 
Actually while a spur from a spur off a ring ,even wired in 4.0mm would not comply with the requirements for ring circuits, and hence should not be done,in practice it should not be a problem.Given that a radial wired in 4.0mm and fused at 32A can supply an unlimited number of sockets you would in effect be spurring a radial from a ring circuit fused at 32A,there would seem little difference.
 
Actually while a spur from a spur off a ring ,even wired in 4.0mm would not comply with the requirements for ring circuits, and hence should not be done,in practice it should not be a problem.Given that a radial wired in 4.0mm and fused at 32A can supply an unlimited number of sockets you would in effect be spurring a radial from a ring circuit fused at 32A,there would seem little difference.

Only problem then is if one leg of the ring fails, then you have a 2.5 with a 32amp breaker/fuse
 

Reply to Spur off a spur in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
192
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Yes, think I will disconnect it again as the 16A protection makes it okay to leave it. Out of caution, check the Electrical Cert. All I've done...
Replies
10
Views
322
Very technical :D
    • Like
Replies
9
Views
590

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top