petewan

can i spur off the cooker switch to a new cooker hood with a fused spur and would 2.5 t/e be ok
any adive you may have i would be greatfull
 
I've recently seen in a loft a 6mm radial off a 32a MCB, feeding 5 Twin sockets then off the last socket there was a 2.5mm to a Switched FCU fused down for a light. Not something you see everyday but i couldn't see any immediate danger. Calcs work out ok.

The only other scenario seen very often is your cooker circuit to isolator, then down to cooker outlet, then next to the outlet a single socket. this being the same idea
 
I believe you are permitted to have overcurrent protection downstream of the point of connection for a reduction in cable size,so has long as there is capability of fusing to limit what the cable can carry with the switched spur then it would be ok I would suggest
 
Hi petewan

Yes it is ok jst try pick an cooker hood with a low current demand as cooker circuits are temperamental at the best of times. Use the same size of cable that supplies the cooker from the FCU to the new FCU for the cooker hood. To supply the cooker hood 2.5mm should be fine.
 

Reply to spur off cooker switch in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

OK. Asking such a basic questions as this (and the answer is simple and I'll provide it in a second), my question to you is do you feel capable...
Replies
7
Views
976
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
431

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top