Can one - providing Max demand is within limits. Cut / break into 25mm Main Tails between Meter and CU. Then Henley block at said join then spur off HBlock and install another Small RCD Garage DB. So effectivley x2 boards in one property are feed off one head/meter. Client has a garage which is attached to the house and he has really done up well new floors etc for a new Gym for his missus. and wants me to install power and lights in new gym. The service head and meter are in the garage. The DB "Old Re wireable" is situated in the house which he has recently had redecorated at a large expense and looks the "Dogs Genitals" My advise when surveying was to replace DB and move it adjacent to Service head he was in aggreement. However he has since come back and said after talks with the missus they want to leave the DB in situ and not have it moved or upgraded on account of wrecking the new decor. I said there will be damage in any case as I still have to get a feed off present DB into garage, he looked gobsmacked and as with all clients they think we either have Blu Tooth Wi Fi electrics or we somehow manage to just push cables through walls ceilings and floors like magic. This is my only solution I dont think there is anything in the regs to say it cannot be done as we are spuring off the consumer side. although I will say it is proberly not good practise.
 
How far from original cu to garage. I would say you would need overcurrent protection at the original cu after you spur of the existing tails.
 
from meter, 25mm tails into 80A fused 2 pole switch/ isolator ( this will give you a single isolation point for the whole installation and overcurrent protection for the tails.) then to henleys. then from henleys to each CU.
 
why?? do not understand why present original CU must now be all of a suddern be protected ??/ tails are +/- 2 meters long
 
Bit over engineered!! Other than offering additional protection why a fused isolator??. Why not a bolt standard 60947/3 DP 100amp isoloator as all the isolator is doing is to enable and provide one to isolate the CU's for maintanance rather than breaking the seal and pulling the supply fuse out everytime to work on CU's. The 25mm tails are already protected by the BS1361 100a fuse. The new mini additional CU will have an RCD main Switch to protect all final circuits from it.
 
Bit over engineered!! Other than offering additional protection why a fused isolator??. Why not a bolt standard 60947/3 DP 100amp isoloator as all the isolator is doing is to enable and provide one to isolate the CU's for maintanance rather than breaking the seal and pulling the supply fuse out everytime to work on CU's. The 25mm tails are already protected by the BS1361 100a fuse. The new mini additional CU will have an RCD main Switch to protect all final circuits from it.


Yes that would be OK too.
 
Have had a read of the BGB its my favourite bedtime read every night as it gets me off to a good nights sleep, works every time. Isolators between meters and CU is still appears a very grey area in domestics. Only speaking to my NIC field Eng about it recently. The issue on old installations is the old on going one about the tails out the meter on the consumer side of the install ARE the resosposibilty of consumer yet they are sealed by the supply co???? Yep going forward new installs and any CU changes where the main fuse is pulled by the Supply Co or with their approval {ha ha :33:} and subject to client willing to pay for the extra gear and labour on CU changes a DP switch should be installed as standard for good practice only not a regulation. Also in the BGB there is nothing to say this is a requirement. The mini GB page 17 Sec 2.2.4 Electricity Isolator Switch It says THE SUPPLIER MAY provide .... The supplier.... not consumer.
Any views on this
 

Reply to Spur off Main Tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
93
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
889
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

yeah so it looks like an old off peak heating circuit to what would have been storage heaters my preference is to remove them completely from the...
Replies
2
Views
407
Sounds more positive.
Replies
8
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top