Spur off a spur in 2.5 T&E off a 32A ring circuit in a utility room running a washing machine & a tumble drier. This was reported on a recent PIR of a rental property and the landlord would like it corrected,

The problem I have is if I install a FCU then the customer can only use 1 appliance at a time (apparently not an option in a busy household!!).

So my solution would be to fuse the spur with a 20A mcb in a small 2 module enclosure, which will protect the 2.5 T&E from overload and still allow use of both appliances at the same time.

Can anybody see a problem with this?

I know its not the norm but to incorporate the utility room into the ring circuit will require ripping up a tiled bathroom floor, which the landlord is very keen to avoid.
 
could you not run a leg below the utility room ceiling ( safe zone) or mini trunking and extend the ring?
 
Done the 20 amp mcb trick myself, can see no problem. In theory if you have 2 single sockets spured from the ring is this different to 1 x twin? But as you know the load may exceed the 20A for a 2.5 best play it safe. As a thought you could limit one of the washing machine socket with a spur if you knew the load. If less than 7 amp 13 + 7 = .... erm 20? Will look tidier if done in a dual box and labelled 'MAX 7AMP' than a small DB.
 
OK , so your solution seems the only way. can't see anything wrong there, only that if 2 machines are on the heating cycle at the same time, they could trip the 20A MCB.or you could sell them a washer/tumbler combined.
 
Not the ring imbalance monster again!!!!!

If 2.5mm2 T&E is rated at 27A (clipped direct) then how can a 20A fused spur overload either leg of the ring?

As mentioned in post 3 it is spured off the upstairs ring which is usually very lightly loaded.
 

Reply to Spur problem? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...
2 3
Replies
43
Views
3K
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top