Spur off a spur in 2.5 T&E off a 32A ring circuit in a utility room running a washing machine & a tumble drier. This was reported on a recent PIR of a rental property and the landlord would like it corrected,
The problem I have is if I install a FCU then the customer can only use 1 appliance at a time (apparently not an option in a busy household!!).
So my solution would be to fuse the spur with a 20A mcb in a small 2 module enclosure, which will protect the 2.5 T&E from overload and still allow use of both appliances at the same time.
Can anybody see a problem with this?
I know its not the norm but to incorporate the utility room into the ring circuit will require ripping up a tiled bathroom floor, which the landlord is very keen to avoid.
The problem I have is if I install a FCU then the customer can only use 1 appliance at a time (apparently not an option in a busy household!!).
So my solution would be to fuse the spur with a 20A mcb in a small 2 module enclosure, which will protect the 2.5 T&E from overload and still allow use of both appliances at the same time.
Can anybody see a problem with this?
I know its not the norm but to incorporate the utility room into the ring circuit will require ripping up a tiled bathroom floor, which the landlord is very keen to avoid.